    I have Hurd a few times now that ring mains will soon be fazed out due to the risk of danger if the ring is split! Is it now advisable to just install radial circuits?

    Thanks for your help
     
  2. highspark
    Offline

    highspark Electrician's Arms

    Rings are still ok. But I always use radials now. Even on kitchens, I just have two radials
     
  3. needasparks
    Offline

    needasparks Electrician's Arms

    Location:
    Essex
    Strange, I heard radials were being fazed out incase they got connected in a ring.

    This story does the rounds every couple of years, usually spouted at college .
     
    • Like Like x 2
  4. leonard
    Offline

    leonard Regular EF Member

    Location:
    South West London
    Ring mains are 11Kv you mean ring final circuit!!!!
     
  5. Guest111
    Offline

    Guest111 Guest

    the way they muck things about i,m suprised we aint gone back to round pin plugs and 1 socket per fuse like years ago.
     
    • Like Like x 1
  6. malcolmsanford
    Offline

    malcolmsanford Electrician's Arms

    I'd be more concerned if they thought Ring final circuits was going to be phased out to be honest. Not a lot of call for ring mains in LV systems, perhaps the odd street lighting circuit, or a large complex HV system.
     
  7. djlander
    Offline

    djlander EF Member

    Location:
    coventry
    So what is best? Ring or radial? I'm due to rewire an office block it's medium sized, each circuit will have no more than 12 double sockets to supply 4 to 5 computers and desks, what would you do? There is about 10 socket circuits in total
     
  8. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    i would use radials , no more than 10 IT% items per circuit. will you have RCD protection? if so leakage could be a problem, also hi integrity earthing is desirable.
     
    • Like Like x 2
  9. djlander
    Offline

    djlander EF Member

    Location:
    coventry
    No RCD protection as it's for IT but do you Mean tuning around and extra earth with the circuit to get the hi integrity earth?
     
  10. widdler
    Offline

    widdler Forum Mentor

    Location:
    North East
    It's been in discussions for many years now. I myself always raise awareness to delegates about the considerations that are made for this to be an issue.
    The last time I brought it up with Geoff Cronshaw I got feedback that the consideration would be to restrict them only to installations under the control of skilled/instructed persons.

    I personally don't think they will ever remove the ring final circuit. If they were, it would require an incident of some kind directly resulting from the area of concern that would motivate the change. IMO
     
  11. djlander
    Offline

    djlander EF Member

    Location:
    coventry
    I maenads running around an extra earth? Stupid iPad's predictive text
     
  12. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    if using radials, you need to run the cpc as a ring-- use separate earth terminals on the sockets and in the DB.
     
    • Like Like x 1
  13. malcolmsanford
    Offline

    malcolmsanford Electrician's Arms

    We always wire, if not using power trac systems a 4mm ring, without RCD protection.

    If your using a radial circuit for high protective current equipment you will need to have your CPC 10mm unless you run a 4mm CPC out in your and a sepearte 6mm back.

    By wiring it in a ring you can drastically reduce cable size. You can in fact wire it in 2.5mm as a conventional ring using T+E or singles but we just prefer 4mm.
     
    • Like Like x 2
  14. Des 56
    Offline

    Des 56 Forum Mentor

    Location:
    Gliese 581C
    Is it not the case that if high integrity earthing exceeds the 10mA,ring finals are the best option
    The cpcs negate the need for a seperate conductor with radials


    How come the replies are quicker from Arabland than Taffland Malc [​IMG]
     
    • Like Like x 2
    Last edited: Feb 18, 2012
  15. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    How come the replies are quicker from Arabland than Taffland Malc [​IMG]

    they've got electrickery in arabland. :45:
     
    • Like Like x 2
Loading...
Similar Threads - Ring mains true Forum Date
Finding out length of cable through measuring resistance. The Electricians Arms Yesterday at 10:32 PM
Ring circuit cable length Electrical Wiring, Theories and Regulations Wednesday at 8:24 PM
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job