Discuss ring testing in the UK Electrical Forum area at ElectriciansForums.net

F

foghorn

whlist testing a ring final socket circuit r1, rn and r2 end to9 end had all the same readings found a spur taken from the ring for an electric towel radiator remove the cpc from towel radiator and end to end test were spot on reconnect towel radiater and r2 end to end was reduced to virtulally equal to r1 and rn any thoughts on this would be appreciated.
 
so do u record the readings with towel rail disconnected as the cpc is no longer 1.67x more than r1, rn or record r2 at lower value which woulnt look right on eic
 
would it be worth mentioning the parallel bath in the coments section stating the towel radiator causing parallal path to explain unusual readings also lowerd the zs reading as well took zs with radiator cpc connected and without lowered the zs value
 
so do u record the readings with towel rail disconnected as the cpc is no longer 1.67x more than r1, rn or record r2 at lower value which woulnt look right on eic

You are testing the Ring Final Circuit fixed wiring, not what is connected to it.
 

Reply to ring testing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi so i am doing a test on sockets on a ring Final circuit for family member. Got my end to ends r1 0.62, rn 0.64, r2 0.97, identified opposite...
Replies
3
Views
2K
Ok. Can you cut a ring in half, add junction box, then run a spur off it? I thought it had to be from a socket? Mate of mine wanted me to see if...
Replies
3
Views
714
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
Hi All, Had a weird one this morning during an EICR. Testing a ring final circuit in a 2 bed flat… kitchen was on a separate ring. With only the...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock