Hi had some rather strange reading today, that i have never seen.
Was carrying out a ring test today on a EICR (r1,rn,r2) and i was getting r1=0.38 r2 = 0.39 and was getting a strange reading of r2=75v???
Any idea why im getting a voltage reading?
 
Hi had some rather strange reading today, that i have never seen.
Was carrying out a ring test today on a EICR (r1,rn,r2) and i was getting r1=0.38 r2 = 0.39 and was getting a strange reading of r2=75v???
Any idea why im getting a voltage reading?

Not sure if you have done a typo on this? r2 = 0.39 - r2 = 75v
 
It's a dead test, should be no voltage, if you still have other circuits powered up, turn then off one at a time and see when the voltages on earth goes, its abit high though to be an induced voltage.
 
It's a dead test, should be no voltage, if you still have other circuits powered up, turn then off one at a time and see when the voltages on earth goes, its abit high though to be an induced voltage.

It does seem high, but on an isolated RFC, I can't see what else it could be. Testers can be sensitive beasts at times.
As always, hard to say anything with certainty without being there.
 
You need to trace the open circuit by checking all socket and spur earth connections, possibly testing the continuity by the long lead test method.
 

Reply to Ring testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All, Had a weird one this morning during an EICR. Testing a ring final circuit in a 2 bed flat… kitchen was on a separate ring. With only the...
Replies
7
Views
1K
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
822
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
After fixing a few CPC related issues on a ring final I got the following results L-L = 0.47 N-N = 0.47 CPC-CPC = 0.69 R1+R2 Tested at 0.31...
Replies
3
Views
1K
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
471

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock