Discuss Ring testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
30
Hi all can you help to settle a argument.

Situation

2 x 4mm in the top of a 32mm. MCB

Option 1

This indicates to me that it is either 2 radials in the same MCB, or a 4mm ring.
A ring continuity test should be carried out to prove that a ring exists or it is 2 radials.
If a ring exists carry on with ring tests. If 2 radials this should be raised further investigation required to identify if an incomplete ring is present, (fault) or it is indeed 2 radials from the same MCB (fault)

option 2

Doesn't matter if it is a ring or not as 4mm is good for 32A carry on and test.


Please vote option 1or 2

my option is 1

yes there are 2 conductors in the MCB
for this posting 4mm conductors throughout the circuit is not an issue.




Quite right should read my post prior to submitting, it's 2conductors. I agree with your option 2 comment I posted this as I am feed up fighting my corner I am looking for a bit of support in my argument
 
Last edited:
Option one, there could be a live end flapping around somewhere. Why would you put 2 x 4mm cables into one MCB? VD/ lowering Zs are the only reasosn I can think of just now
 
How many 4mm cables are in MCB?

Cant vote for either. Option 1, i assume you have 2 x 4mm cables, and instead of testing it properly to find out, you are guessing..

Option 2, gives me the impression that you don't really understand what you are doing.

You will get some real flack in response to this post.

Cheers...........Howard
 
And do you know if the whole circuit(s) is/are in 4mm, or perhaps just the first leg(s) (I came across this once)?
 
option 1. it's either a ring or 2 radials. determine which it is. if a ring, then carry on with the usual tests for a RFC. if 2 radials, then test as 2 radials and preferably separate them to separate MCBs.
 
This may have been a 4mm radial origanaly but some one may have added some extra sockets and decided this was the easiest and least desruptive way of doing it. You can do it this way according to the regs.

Jay

Obviousley, futher testing is required to determine if its a ring or not!!
 
I think the bottom line is you have to know what the circuit(s) is/are and test accordingly (option 1), you can't just make assumptions or not care (option 2).
 
Are you sure it's 4mm if its old cable it does look thicker/ stranded cable. First thing you need to do as others have said is carry out the sequence for testing a ring eg end to ends to see if there is a ring if not, and there isn't a break then I would assume that it is possibly two radials and personally I would split onto two 16a breakers. But that's just my way of working
 
How can you say just carry on 4mm is good for 32A the green book may suggest that it is. However once you take into account downrating factors such as grouping or thermal insulation it will not be. The point I wea trying to get to was that we donot know why it was installed this way. There is a strong possibility that 4 mm may have been designed to comply with earh loop values. Volt drop. Or to compasate for any derating factors.
My feeling is that if you see 2 conductors in the top of a MCB there is a possibility that it may have been designed as a ring and this should be confirmed. If it is an open circuit further investigation should be carried out to determin why 2 circuits are fed from 1 MCB.
It may be that you have 2 high load circuits in 1 MCB and that a 32A MCB is to small.
 
In my opinion if u see two cables in one breaker irrespective of size I would first test end to end.
I have seen 2 x 4mm in a breaker recently feeding a high end power hungry entertainment system. Amazing how much power it used
 
First establish whether it's a ring or a radial, then if it's a radial, establish if the CCC is adequate to be protected by a 32a breaker. Having 'two radials' in one breaker isn't an entirely accurate statement either, it is one radial circuit with two branches, and although perhaps not always the best practice, it can be done with the blessing of the IET. For all you know, one of those cables might only supply one double socket!
 
How many 4mm cables are in MCB?

Cant vote for either. Option 1, i assume you have 2 x 4mm cables, and instead of testing it properly to find out, you are guessing..

Option 2, gives me the impression that you don't really understand what you are doing.

You will get some real flack in response to this post.

Cheers...........Howard

the point I am making is that until you do an ring end to end you must assume it is a ring.
 
cobblers. until you test it you can't assume anything other than that there are 2 cables in 1 breaker.
By assuming that it is a ring the first test you would carry out is a ring continuity test
This will prove if it is or is not a ring.
Once you have done you then decide on your next test.

If you do not assume it is not a ring what would be your first instinctive test?
 
By assuming that it is a ring the first test you would carry out is a ring continuity test
This will prove if it is or is not a ring.
Once you have done you then decide on your next test.

If you do not assume it is not a ring what would be your first instinctive test?

My first instinst says that the OP doesn't know what he's doing
 

Reply to Ring testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
823
HI All, I am building a new house (self build) and have my part P so am running the cabling. My reading of the regs says that any appliance of...
Replies
18
Views
4K
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
650
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
796

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock