Is there any better way of doing this?
1 DNO Supply - 100A
2 Buildings - not connected to each other.
DNO on Main House - PME Supply
Holiday Cottage run by 25mm SWA (2 Core) from House Supply (underground)

25mm running 6m from DNO to CU - 100A Iso fitted
2nd Iso for Holiday SWA Supply - 80A
Holiday Cottage on TT - unless it can go to PME - to my memory it can't

Metal CU in Main House all RCBOs
Insulated CU in Holiday Cottage on split load

Any Thoughts??
 
How far are they apart?
Not 100% but if the distance isn't too great, earth loop impedance ok (and suitable protection installed) then a 16mm2 earth should be enough to extend the equipotential zone?
 
How far are they apart?
Not 100% but if the distance isn't too great, earth loop impedance ok (and suitable protection installed) then a 16mm2 earth should be enough to extend the equipotential zone?

Only 10m apart - but their is no connection apart from the electrical cable and water pvc pipe between them.

My understanding was if they are not connected together structurally then a TT System is required
 
I'm shattered so again admit I may be talking out of my rear end.....
Neither of them is a caravan so PME earthing isn't prohibited by BS7671:2008(2011)
How is it any different to the DNO looping the supply between 2 heads?
10 metres is enough that you couldn't touch extraneous conductive parts, but close enough that the TT might have problems given the PME is so close by?
(e.g. the situation someone quoted either here or on the IET boards - customer supply was TT but neighbours close by were all PME, DNO came out and changed the customer to PME)
The way I look at it is...as long as the earth loop is low enough resistance then using the supplier earth is going to be safer than using a Rod. Plus your splitting the tails so the effect of one install shouldn't affect the other (well unless the cutout fuse blows...) Essentially its no different to a detached workshop etc??
Though freely willing to admit I might be wrong.......
 
Problems - what kind of problems - cant imagine how a TT being close to a PME could cause problems unless a fault occurred.

At the end of the day the Earth is only there as a safety backup in case a fault does occur - it serves no other purpose
 
it serves no other purpose
Except when it part of it is also the neutral, in which case it carries current, experiences voltage drop, takes on various potentials at different places...
 

Reply to Running 2 supplies from 1 DNO Head in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
Hi, I’m an industrial electrician, so when it comes to DB regs and such my experience on them is a little limited. I need 2 x 16A 3 phase supply...
Replies
1
Views
677
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
518

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock