Search the forum,

Discuss s y cable advantages and disadvantages in the Electricians' Talk | All Countries area at ElectriciansForums.net

stumas

-
Reaction score
1
why would you use yy cable for general lighting and power in a commercial environment over twin and earth, any ideas?

what would be advantages and disadvantages any help would be grateful. thanks sorry yy not sy
 
Last edited:
It offers better protection than T+E but not as good as SWA. Personally I’d use SY where I needed protection but with a degree of flexibility. Being honest I don’t like the stuff but at times needs must. The correct glands are relatively expensive and finger rippers if not made off correctly.
 
The screen can be bonded, it will not be enough to replace the CPC, but can trip an RCD if the wire is cut. So slight safety benefit.

If you are worried about retards, it looks strange so they might treat it with more care.
 
If you are worried about retards, it looks strange so they might treat it with more care.

I'm one of them and think SY looks real pretty, I like to hold it to admire the geometric shapes under the plastic... then I like to gnaw on it 'til my lips hurt!

The OP changed the cable type in question to YY, by the way.
 
I seem to remember reading that the screen is earthed to stop 'noise' being transmitted to adjacent cables, and places like airports use it when run alongside data cables etc.
 
I think T&E should stay in the domestic game, the house-bashing profession!

I'm not familiar with commercial but I've seen sparks use T&E in conduit and across cable tray. It looks crap. Stick to keeping it buried in plaster or clipped to joists in attics!

I'm assuming lots of conduit, tray and basket in commercial installs. Twisted T&E looks plain awful on tray, especially when chafed and better cabling solutions are available. Conduit is suited to singles, not chunky oval cable.
 
Last edited by a moderator:
It is great for connecting the large resistors we use for DC current sensing to remote operator panels as the small output around 50-75mV needs to be well screened but also has to survive. I don't use it for much else other than temporary lighting setups.
 
I assume you’re referring to shunt resistors. Why do you need to screen the signal? If it’s a large DC drive the signal will be very stable.

PS I hope you fuse the O/P from the shunt, wouldn't like to be around to see 900A trying to get through a bit of 2.5
 
Last edited by a moderator:
I've used it a lot to screen motor supplies that are on inverters. Supposed to stop RF from other cables such as 4-20setc? Although I practice this I'm not entirely convinced it makes any difference lol. SY this is.
And I totally agree to keep t and e well out the industrial game
 

Reply to s y cable advantages and disadvantages in the Electricians' Talk | All Countries area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock