porterelec

I'm on a job that the previous sparks made a hash of and I'm sorting everything out and finishing the rewire. The client wants to put a sauna in next year and he requires a supply for it. Does anyone have any recommendations as to suppliers or know what size load I am best accounting for the supply? Many thanks PME
 
3-6kw I'd guess depends on room size etc.
 
The cable will vary depending on the location and size of the sauna but if you are installing for an unknown load then for a sauna they are very unlikely to exceed 8kW (generally about 3kW) so you could install a 6mm² cable up to the point outside the proposed room/location, then you can leave a connection point there ready for a heat resistant cable to feed the heater in the sauna.
Even is it is a 3kW heater you can then just put in an appropriate MCB for the load, if it does turn out to be a huge heater then you are covered and (so long as the run is not huge) the cost difference is only a few pounds and cheaper than reinstalling a cable.
 
Thanks very much guys, that pretty much confirmed my suspicions and as the run is only 15m so it would make sense to just put a 6mm in.

Regards,
PME
 

Reply to Saunas in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
964
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
779
This is quite lengthy so get comfy... I had a bizarre call out relating to a job I attended about five years ago. The situation was they were...
Replies
11
Views
1K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock