Just trying to double check if there's a reg suggesting a 3phase circuit should have over-current device that disconnects all line conductors at once? Got an old rewireable board supplying 3phase motors with 3 individual fuses.

I'm looking at 530.3.1 ...................

Can anyone confirm this?

Thank!!
 
Not all three phase circuits are protected by a device that disconnects all three phases, you said in your post that you have a large rewireable D/B thats quite common in industrial installations, most final circuits (three phase motors for example) would have their own individual protection, which would sense an over current in one of the phases. should one of the main phases go open circuit 530.3.1 deals with this scenario (a contactor motor starter) as an example. Your board should supply the motors via a starter.
 
Agree as Pete999 has stated...

There are 3 phase switch fuses/fuses switches etc, that use special striker fuses, that release a short rod. So that when any of the fuses operate, the released fuse rod hits a striker plate that opens the load contacts to all 3 fuses.
 

Reply to Separate fuses for 3phase supply in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, just looking for advice. Ive been to look at a Fire alarm install job. While checking where i will take my supply from. 3 phase sub board, i...
Replies
20
Views
1K
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
616
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
984
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
721

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock