davelerave

when separating 13amp sockets on different phases by 2/2.5m

-the only concern is physical separation of the sockets and not leads and appliances?


am i right in thinking any risk to customers/users from appliances on different phases is very small?
 
when separating 13amp sockets on different phases by 2/2.5m

-the only concern is physical separation of the sockets and not leads and appliances?


am i right in thinking any risk to customers/users from appliances on different phases is very small?

You are right it is very small.

So small that even the label requirement has the words 'exceeds 230V to earth' in amendment 1 (how many installations do you work on with a nominal voltage exceeding 230V to earth?)

For now though, 514.10.1 uses terms such as 'reached simultaneously' and 'exceeding 230 volts' so best to label.
 
Last edited:

Reply to separation of 13amp sockets on different phases in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
516
Hello All done an EICR on a small office around 5 years old someone has added extra socket circuits from new to suit layout. they have added...
Replies
6
Views
1K
hi. would appreciate advice from any electricians. am trying to replace a 13amp [35 year old MK] wall socket but the terminal cage in all the...
Replies
11
Views
1K
Hello, I have a hypothetical question (I'm an electrical engineer) to better understand RCBOs and how they are used in the USA. Let's say I would...
Replies
9
Views
961
Hi all I am new to this forum and hope this is right placed and of interest. I would like to make a setup with one or more impulse relays...
Replies
9
Views
997

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock