Discuss Seperate Earthing circuits in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

R

robmark1976

Hi hope you can help, we have just carried out a survey of an office floor that we are due to fit out and the floor boxes and VAV units don't have separate Earth cables to them, even though there are numerous circuits the earth relies on 1 earth cable bolted onto the metal trunking by the distribution board and then linked to all the different circuits and not separate earths, I know this does not comply with BS7671 but the consultants wants me to be detailed and quote the regulation from the REGs to show this does not conform, Thanks Rob
 
the metal containment can be a common cpc for all circuits contained within it.
 
I thought all individual circuits had to have there own PC and not share an earth with other circuits or am I wrong?

Not when a full metal containment system (eg, trunking and conduit) is being used to distribute several circuits within....

I'll put money on that metal containment providing a far better Zs value than your 1mm and 1.5mm separate CPC's.
 
Last edited by a moderator:
Hi hope you can help, we have just carried out a survey of an office floor that we are due to fit out and the floor boxes and VAV units don't have separate Earth cables to them, even though there are numerous circuits the earth relies on 1 earth cable bolted onto the metal trunking by the distribution board and then linked to all the different circuits and not separate earths, I know this does not comply with BS7671 but the consultants wants me to be detailed and quote the regulation from the REGs to show this does not conform, Thanks Rob

A very good illustration of the dangers of being self appointed electrical police without knowing the regulations or even where to find the appropriate regulations. Humble pie beckons.
 
Hi hope you can help, we have just carried out a survey of an office floor that we are due to fit out and the floor boxes and VAV units don't have separate Earth cables to them, even though there are numerous circuits the earth relies on 1 earth cable bolted onto the metal trunking by the distribution board and then linked to all the different circuits and not separate earths, I know this does not comply with BS7671 but the consultants wants me to be detailed and quote the regulation from the REGs to show this does not conform, Thanks Rob

Now i wonder WHY the project consultants want you quote the regulation from BS 7671?? Because they already KNOW there isn't one, and that there own site survey has already confirmed compliance maybe??
 
Hi hope you can help, we have just carried out a survey of an office floor that we are due to fit out and the floor boxes and VAV units don't have separate Earth cables to them, even though there are numerous circuits the earth relies on 1 earth cable bolted onto the metal trunking by the distribution board and then linked to all the different circuits and not separate earths, I know this complies with BS7671 but the muppets in suits wants me to be detailed and quote the non-existant regulation from the REGs to justify their existence, Thanks Rob

correction applied for you
 

Reply to Seperate Earthing circuits in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I'm getting an old fuse board upgraded in an office block. The electrician has just told me that most of the circuits don't have earth cables...
Replies
44
Views
3K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Some friends are setting up a metal workshop inside a shipping container, on site at a commercial building that rents out studios, workshop space...
Replies
9
Views
1K
I've just started at a new church and the electrics are bit of a shambles. I'm not going to be touching them as I'm not qualified, but one thing I...
Replies
14
Views
5K
Hi, I have a property that I was looking to rent out. Its 12 years old property so relatively new. I had a EICR done from a qualified electrican...
Replies
59
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock