sorry this may seem obvious. All of the shower manufacturers stipulate the main swith must be rated > 80Amps for connection of their showers in their instructions, so when you fit a seperate Shower C.U. due to the old board either being full or a wylex 3036 does this mean that the rating of the seperate shower C.U. RCD main switch has to be 80AMPs. as most shower C.U come with a 63A 30ma RCD mainswitch. im thinking this cant be right and this 80A mainswitch figure applies to a main C.U. anyone confirm my thinking.

to my mind the seperate shower cu is supplying one fixed load so as long as its rated above the rating of the shower it should and will be fine. just wanted to check if im missing something
 
i would tend to agree with you. most shower isolators are only 45A anyway.
 
sorry this may seem obvious. All of the shower manufacturers stipulate the main swith must be rated > 80Amps for connection of their showers in their instructions, so when you fit a seperate Shower C.U. due to the old board either being full or a wylex 3036 does this mean that the rating of the seperate shower C.U. RCD main switch has to be 80AMPs. as most shower C.U come with a 63A 30ma RCD mainswitch. im thinking this cant be right and this 80A mainswitch figure applies to a main C.U. anyone confirm my thinking.

You're right, that rating would be for an existing consumer unit supplying the shower, to allow for the combined loading of the existing circuits (cooker etc.)
 

Reply to seperate shower CU in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock