Hi

I'm working on a distribution system where the main s/w is a 200amp 4 pole mcb with a bolt on adjustable rcd. The rcd needs to be set to 300ma and have a time delay for discrimination purposes.

Can anyone advise to which setting on the ms adjuster I use? The ms scale goes from 0-60-150-310.

Cheers

Wozzit
 
There's plenty of information about the NS250n on the Shneider site.
you need to determine what you're discimiating against as SPARTYKUS said.
 
Any chance of posting a photo of this MCCB with a close up on setting dials?? As a starting position i'd normally say around 100mS, but your set-up doesn't seem to allow that time delay.... On a standard S type RCD, tripping times are between 130 and 500 mS at x 1 sensing...
 
Oldtimer, there are two dials on the rcd part of the switch one in ma and the other in ms. The ma dial is set to 300ma although you can adjust it all the way to 10 amps if needed. The ms dial is adjustable between 0-60-150-310 ms, this is the time delay setting.

Needasparks, yes your right the installation is on a farm. I asked the dno whether they could convert the supply to TN but they said no due to the type of building the supply terminates in. In this case a metal shed in the middle of a field.

Regarding the enclosure being metal and not being rcd protected I've done all I can to limit the chances of an earth fault occuring on the case. Double insulated tails enclosed in plastic trunkin, tails not in contact with the enclosure, the switch itself is class 2 and a bit of perspex covering the metal face of the enclosure with cut outs to adjust dials. I tried getting hold of a plastic enclosure but no luck.

Engineer 54, having problems uploadind a photo of vigi unit but check out the following link
LV431536 - schneideronline.com.au this bolts on to the mccb

Wozzit
 
Discriminating against a 300ma rcd further down stream
You are discriminating against a 300mA RCD downstream so you need to know how fast this trips, if it is a time delay one and set to say a delay of 60ms your RCD would need to be set to 150ms, assuming it is the same unit.
The units are coordinated so that a 60ms delay will trip in less than 140ms so 150ms delay would discriminate.
If the one downstream is not time delayed then yours could be set to 60.
Effectively the downstream one must trip first in order to avoid nuisance tripping.
I assume the controls are like this:
NSX250 plate.jpg
 
Cheers Richard, yes that is the exact same control panel.

Downstream RCD is a different make to the Merin above and is not time delayed.

So to sum up its a case of testing the downstream RCD, finding what its tripping time is and adjusting the vigi accordingly.

Wozz
 
Again, no expert but not sure it'll work that way? Think the RCDs are wrongus wayus roundus.

I suppose it depends how quickly the up front one trips.

I think the S type 100ma ones in older TT domestic (& other) installs were put up front with about a 0.1seconds as this is long enough to be sure of discrimination...?

The way youre set up you'll be relying on the characteristics of a non time delayed RCD(if I read you right!) to be particularly slow....

And havent looked at the dials yet but if up front RCD trip in normal times (eg 35ms), not sure you have the legroom to discriminate.

Again I am no expert but find this an interesting thread and look forward to more learned input & your final resolution!


I'm wondering if the RCDs could be changed round to Mr time delay is up front
 
Cheers Richard, yes that is the exact same control panel.

Downstream RCD is a different make to the Merin above and is not time delayed.

So to sum up its a case of testing the downstream RCD, finding what its tripping time is and adjusting the vigi accordingly.

Wozz
From Spartykus post I would like to say that the arrangement I think you have is:
Supply.....Your TDRCD......non time delayed RCD......Equipment.
I.e. the time delay is upfront and closest to the supply.

You cannot just measure the trip time as conditions could be different under a fault and change the trip time. You have a different make downstream so coordination is more difficult since they will not be designed to the same characteristics. You need to know the tripping characteristics of the down stream device and your RCD and work out the value of delay that will ensure discrimination.
GN3 recommends that the trip time of an RCD does not exceed 300ms if it is not time delayed, however the RCDs you are using may have different characteristics.
For instance, I do not know the model of RCD you have but this is something similar (may be the same) that specifies the trip times for the RCD
vigi characteristics.jpg
As you can see the maximum trip times are coordinated for each setting (and are considerably less than 300ms when not time delayed).
You will need to find similar information for both your RCD and the down stream one and if you have a maximum tripping time downstream of 200ms then your RCD could be 300ms and so on.
Do some research, get on google, find the information for your devices, apply them to your situation and you are then sorted.
 

Reply to Setting an adjustable rcd? in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi all, need some opinions on the following please> Origin is a three phase 60A TN-C-S supply.it goes into a changeover switch (small PTO driven...
Replies
59
Views
6K
S
I will post the answers on here in a few day or if you really want to know PM me and i will send them. Example Questions for 2382-10 1. The...
Replies
1
Views
2K
sxsparky
S
E
I think I've Posted this before, but I've just updated it. Some of the sparks where I work still get a little confused of what the different areas...
Replies
58
Views
77K
Here is a sample paper for the 2382-20 (the update to 17th) answers to follow, enjoy!!! Sample 2382-20 (update for 17th 30 questions) Answers...
Replies
13
Views
29K
maddfridge
M

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock