Discuss Shed and jacuzzi advice in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi, I’ve been asked to install lighting and 3 sockets (one of which is for a fridge) in a wooden shed. Due to location of consumer unit the only feesable option is to use the feed from the Jacuzzi which is on the non RCD side of the CU using a 40A MCB with 10mm Twin & Earth cable and own isolator switch.

Total length of cable would be 25 meter’s, 19m indoors and 6m outdoors leading to the shed (not buried) to mini CU with RCD protection

The jacuzzi is 6Kw and fridge 2Kw so 40A mcb will handle load and should be most used at anyone time.

My question is, if I extend the 10mm t & e that inside the house with 6m of 10mm SWA outside the house does it alter my cable calculations as they have different reference methods?
 
calculate based on the worst case. what ref. method is the existing?
 
looking at the build, which is relatively new, the size of cable and the worst case scenario of the Jacuzzi enclosed in conduit in thermally insulated walls as other methods e.g. show a 6mm cable size is suitable
The SWA will have to be clipped to or under decking which is above ground by a couple of foot
 
A 6mm cable might be suitable for the load but im pretty sure it wont wont the current carrying capacity for a 40A mcb once derating factors have been taken into account. Also i was always under the impression that a jacuzzi needed rcd protection as most manufactures recommend als if you are putting sockets for genaral use in the shed these will also need to be rcd protected.
 
a lot of jacuzzis come with an integral RCD. ours has a 10mA RCD moulded plug on it's LV cable.
 
it's round the back that 'er indoors likes to chill.

022.jpg
 
The CU in the shed will have RCD protection and the Jacuzzi Isolator has built in RCD protection.
I haven’t decided on the connection yet tbh, either at the isolator or extend the cable slightly before the isolator so the Jacuzzi is a spur.
 

Reply to Shed and jacuzzi advice in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
496
Hi all Now being upfront I am not a sparks. I am about to have some work done by a friend (certified) and as he is doing me a favour I want to as...
Replies
5
Views
1K
Hi all, I'm planning on adding some lighting to an old stone shed, there's currently a 2.5mm² SWA supply to the shed only supplying one IP rated...
Replies
7
Views
1K
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock