• IMPORTANT: Please note that nobody on this forum should be seeking from or providing advice to those who are not competent and / or trained and qualified in their field (local laws permitting). There is a discussion thread on this global industry-wide matter HERE. This also has more information about the warning with regards to sharing electrical advice in some countries. By using this forum you do so in agreement to this.

Discuss Should be straightforward, but..... in the Central Heating Systems area at ElectriciansForums.net

Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:   American Electrical Advice Forum

polo1

-
Arms
Reaction score
633
Changing a faulty Drayton SM1 mechanical programmer with a Siemens RWB 1007 programmer (both single channel) serving a Ferroli DOMIcompact F24D combi boiler.

System appears to wired - mains, programmer, thermostat, boiler. The original back plate serving the Drayton had a link between L & 1, with the thermostat feed in 3. Keeping this arrangement with the Siemens, the thermostat (and hence the boiler) has a permanent feed even when the programmer is switched off.

Tried various permutations, but only ever get perm feed to thermostat with the programmer off, or no power to thermostat, irrespective of the setting of the Siemens programmer.

Confused!
 
Changing a faulty Drayton SM1 mechanical programmer with a Siemens RWB 1007 programmer (both single channel) serving a Ferroli DOMIcompact F24D combi boiler.

System appears to wired - mains, programmer, thermostat, boiler. The original back plate serving the Drayton had a link between L & 1, with the thermostat feed in 3. Keeping this arrangement with the Siemens, the thermostat (and hence the boiler) has a permanent feed even when the programmer is switched off.

Tried various permutations, but only ever get perm feed to thermostat with the programmer off, or no power to thermostat, irrespective of the setting of the Siemens programmer.

Confused!
Perm live to 2 and switch live to boiler from 4. If you look at the manual it says if using 230V switching then link live to 2. 1 and 3 is used for the permanent live to the boiler and is normally closed so it disconnects the boiler when the service interval timer kicks in and opens the contact between 1 and 3. This way the boiler can't be used until it's serviced and reset.

Should be straightforward, but..... IMG_1041.PNG - EletriciansForums.net
 
Thanks all. After a bit more head scratching, I discovered that one of the programmer pins was not making proper contact with the backplate connection ( serves me right for not replacing the backplate!).
Now sorted & working.
 