It is allowed that the mcb can be selected that it's higher than the ccc of the cable when overload protection isn't necessary.
As an example, A ccc of 39 amps but protected by a 40 amp mcb would be allowed if the shower had a fixed load Of say 37 amps.
There's no overload issue in this example and this arrangement is allowed by bs 7671.
 
As an aside, you normally find that a "9.5kw" electric shower is built to take a 6mm T&E try and introduce a 10mm T&E and it distorts the casing the terminals are not man enough to take it but what the hell !!
 
An Overcurrent Protective Device (OPD) might be used for three reasons.
1/ Overload.
2/Short circuit.
3/Earth fault.
If the load is fixed such as a shower then only 2/ and 3/ apply as to the OPD clearing short circuit and earth faults.
If the load does not exceed the cable rating then all ok.
We used to quote power at 240v nominal therefore 9500/240 =39.58 amps.
If the same purely resistive load is run at 230v it would be37.92amps =8.72KW.
Now we officially declare 230v instead of 240v (although the actual voltages have never changed).
Was the power rating quoted at 230v or 240v?
 
Last edited:
65 posts about a bleeding shower. do as I do. I have a bath every Xmas, whether I need one or not. saves a fortune on the leccy.

oh, and you can't read a book, smoke a smoke, or drink a whiskey in a shower,

a bit like the lady who demanded a refund on a packet of Tampax, as she pointed out

" Tried you product. it's useless. I still can't swim or ride a bike".
 
An Overcurrent Protective Device (OPD) might be used for three reasons.
1/ Overload.
2/Short circuit.
3/Earth fault.
If the load is fixed such as a shower then only 2/ and 3/ apply as to the OPD clearing short circuit and earth faults.
If the load does not exceed the cable rating then all ok.
We used to quote power at 240v nominal therefore 9500/240 =39.58 amps.
If the same purely resistive load is run at 230v it would be37.92amps =8.72KW.
Now we officially declare 230v instead of 240v (although the actual voltages have never changed).
Was the power rating quoted at 230v or 240v?
If it's quoted at 230V then at 240V it's 43A and 250V it's 45A
Even worse if it's quoted at 220V (which is often still the case with some imported kit) then at 240V it's 47A which exceeds the 1.45 factor
 
If it's quoted at 230V then at 240V it's 43A and 250V it's 45A
Even worse if it's quoted at 220V (which is often still the case with some imported kit) then at 240V it's 47A which exceeds the 1.45 factor
If it's 6mm cable and on a 40 amp mcb how is the 1.45 factor exceeded?
6mm if it's clipped direct is 47 amps.
47 x 1.45 = 68.15 amps
40 amp mcb x 1.45 = 58 amps
So what's the problem? Cable will not be overloaded.
Remember I2 needs to be equal to or less than 1.45 x Iz.
 
If it's 6mm cable and on a 40 amp mcb how is the 1.45 factor exceeded?
6mm if it's clipped direct is 47 amps.
47 x 1.45 = 68.15 amps
40 amp mcb x 1.45 = 58 amps
So what's the problem? Cable will not be overloaded.
Remember I2 needs to be equal to or less than 1.45 x Iz.
if you avataar is a sample of the fuses you use, then no wonder they don't blow. :D:D:D
 
6mm cable holds 34amps if in a wall which usually always is - therefore cable should be protected by 32amp breaker to prevent cable overheating. If a plumber decides to install a 10kw shower the cable is protected, (shower will trip out) and you are covered. Job done
 
6mm cable holds 34amps if in a wall which usually always is - therefore cable should be protected by 32amp breaker to prevent cable overheating. If a plumber decides to install a 10kw shower the cable is protected, (shower will trip out) and you are covered. Job done

What sort of wall ?
 
6mm cable holds 34amps if in a wall which usually always is - therefore cable should be protected by 32amp breaker to prevent cable overheating. If a plumber decides to install a 10kw shower the cable is protected, (shower will trip out) and you are covered. Job done
Nearly a year later I would like to think the problem has been resolved by now.
 

Reply to Shower EICR Code- 9.5kW- 40amp mcb!. De rate MCB to 32 or rewire cable to 10mm in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello guys n gals, Did n EICR other week in a flat where the shower circuit was 40A mcb with RCD protection, 6mm cable. Only about 10M run. The...
Replies
14
Views
3K
Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...
Replies
13
Views
621
Another what code! This is in conjunction with an EICR I have just carried out. 9.5kW shower on 6mm and 32A MCB. Been in place for a long time...
Replies
8
Views
3K
Hey all, Could do with some help. I had a company recommended to me who quoted me to do an EICR on my rental property. (£265). I thought this...
Replies
5
Views
2K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock