If the cable is clipped direct then as Table 4D1A states the cable is rated at 47 amps.

Chances are though that the cable is run from the Pull switch through the loft under the insulation therefore reducing the current carrying capacity drastically. The OP could clarify this.

We have always (old company policy and what we see as good practice) run any shower >9.0KW on a 10.0mm cable or chose a different shower. Better to be safe than sorry
 
AS a 10.5kW shower pulls 43.5A and you are using a 45A ocpd then what's the problem with using 6mm?
6mm has a ccc of 47A provided the installation method is C. If it passes through any insulation in the loft, then re-route it so it's on the woodwork in fresh air. Use 4 inch pipe to provide an air space where the cable must pass though the insulation layer.

Beat me to it DOH!!
 
And you need to follow manufacturers instructions which usually say they want a 10.5kw on a 50a breaker which if 6mm carries 47 amps best case is not good enough so you would need to upgrade to 10mm anyway to adhere to the instructions, and probly for warranty reasons too if anything goes wrong with it in future
 
And you need to follow manufacturers instructions which usually say they want a 10.5kw on a 50a breaker which if 6mm carries 47 amps best case is not good enough so you would need to upgrade to 10mm anyway to adhere to the instructions, and probly for warranty reasons too if anything goes wrong with it in future

You are so right. Most manufacturers' instructions are now telling you minimum cable size as well as breaker size.
Also, we keep hearing about "clipped direct" cable ratings, but tbh I have never seen a shower close to the CU AND only clipped direct. Once you apply even small rating factors it is amazing how much larger the cable must be to comply with regs.
 

Reply to Shower install in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock