Posting a message to the forum will remove the above advertisement
  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.

Shower Issue

Discussion in 'Electrical Forum' started by Englishman, Apr 30, 2014.

Discuss Shower Issue in the Electrical Forum area at ElectrciansForums.co.uk.

Thread Status:
Not open for further replies.
Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. Englishman
    Offline

    Englishman Electrician's Arms

    Location:
    Surrey
    Went to a job today as a follow on from another sparks on our firm. Was a "fishy smell" reported, and was advised that the cable was undersized.

    Get there today and find a 6mm cable, 40a MCB and 9.5kw shower; and this in the isolater...

    [​IMG]

    Now, the supply voltage is 242, the cable run goes from the board, up to the first floor in a piece of conduit in the wall (reference method A) which rates at 34a, and then up a void behind the shower, clipped direct (reference method which rates the cable at 47a.

    Obviously the cable at the lowest part (bit going through conduit) is carrying 39.25a; which is greater than 34a, and they're sending me back to put a 10mm supply in tomorrow. My argument is that the damage to the cable has been caused by a loose neutral at the isolater and that although the cable is undersized, it's not massively bad and probably wouldn't cause a huge amount of issues if the shower was run normally.

    Opinions please boys....
     
  2. topquark
    Offline

    topquark Electricians Arms Member Forum Mentor

    Burning is only on the neutral term, so defo down to a poor neutral termination. You've been told to replace, so you should. However, I doubt it draws its rated max load in use!
     
    • Like Like x 1
  3. Meggerman
    Offline

    Meggerman Guest

    I'd just replace switch if it were me, the damage was caused by loose termination. They run for such a short time, in reality 6mm will never be a problem. There are plenty of 9.5kw showers on 32A MCB's.
     
    • Like Like x 2
  4. topquark
    Offline

    topquark Electricians Arms Member Forum Mentor

    Borderline, depending on applied derating, 6mm is good to 40A CCC before derating...depends how where it's run....putty they don't do 35A breakers ... bet it would hold!
     
  5. topquark
    Offline

    topquark Electricians Arms Member Forum Mentor

    I've clamped a few when running ... pull a little more than 32A on start up (but not much).
     
    • Like Like x 2
  6. Pete999
    Online

    Pete999 Forum Mentor

    Location:
    Northampton
    Business Name:
    None
    Loose Neutral by the looks of it
     
    • Like Like x 1
  7. 7029 dave
    Offline

    7029 dave Forum Mentor

    Location:
    bedfordshire
    I go with that Pete.
     
  8. robd
    Offline

    robd Electrician's Arms

    Location:
    East Anglia
    Personally always advise customers to leave switch in the on position on the isolator which stops the wear and tear...whether or not they listen to me is another thing
     
  9. GMES
    Offline

    GMES Hairy and proud Staff Member Admin

    I go with that Dave
     
  10. Englishman
    Offline

    Englishman Electrician's Arms

    Location:
    Surrey
    I know it's the loose neutral which has caused the issue that I responded to.

    What I'm referring to the forum is how much it actually needs to be changed. And how much of an issue would be caused by leaving it.
     
  11. SirKit Breaker
    Offline

    SirKit Breaker Guest

    Definitely, i have done loads of these. just hope that whoever installed it, left plenty of cable so you can pull it well clear of the ceiling to re terminate it a bit easier!

    Cheers..............Howard
     
  12. Hawk81
    Offline

    Hawk81 Electrician's Arms

    Location:
    Northern Ireland
    I would say it might not be a loose neutral connection. The other possibility is the pull cord itself is at fault. I have replaced 4 GET 45amp pullcords in this last week. All looked identical to that in the picture. I do a lot of maintenance for an estate agent and the most of the calls I get are showers and 9/10 its the pullcord. Try a different make as well as insuring all terminations are tight.
     
  13. Englishman
    Offline

    Englishman Electrician's Arms

    Location:
    Surrey
    As I wrote in the first post, I know that the problem is at the isolator.

    What I want discussed is the cable suitability. The only part where it doesn't comply is the metre drop down to the CU. Would you leave the cable and mcb, downrare the mcb or just rewire.

    Highly likely I'll have to rewire tomorrow but I just think it's unnecessary.
     
  14. topquark
    Offline

    topquark Electricians Arms Member Forum Mentor

    I would replace it. That's what you were asked to do. Maybe there's a pending upgrade in plan to 12KW in the near future.
     
    • Like Like x 1
  15. Lagentium
    Offline

    Lagentium Regular EF Member

    Location:
    West Yorkshire
    Will a 10mm twin fit up the conduit? They are quite large by twin and earth standards. I've changed them too in the past, I think it doesn't help that they get twisted all over the show to get them to fit back if someone has fitted a box that's too shallow and it loosens the connections slightly
     
Loading...
Similar Threads - Shower Issue Forum Date
Downgraded from a 9.5Kw shower to an 8.5kw one. Need to change wires/fuse/switch as well? Electrical Wiring, Theories and Regulations Saturday at 2:11 AM
Domestic Shower tripping mcb after being used Electrical Forum Jan 10, 2019
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job