So we're looking at B for the conduit run and C for the rest. 41a and 47a, shower will pull 39.25a at it's maximum.
Discuss Shower Issue in the UK Electrical Forum area at ElectriciansForums.net
I know it's the loose neutral which has caused the issue that I responded to.
What I'm referring to the forum is how much it actually needs to be changed. And how much of an issue would be caused by leaving it.
I would say it might not be a loose neutral connection. The other possibility is the pull cord itself is at fault. I have replaced 4 GET 45amp pullcords in this last week. All looked identical to that in the picture. I do a lot of maintenance for an estate agent and the most of the calls I get are showers and 9/10 its the pullcord. Try a different make as well as insuring all terminations are tight.
Did you try putting a clamp meter on it to see what current the shower was pulling on full power?
what brand do you use? we tend to use 45amp crabtree pullcords.
the only problem we have had is from time to time it doesnt always click properly but a quick swap and crises averted
Considering he said GET 45amp pullcords i'd hazard a guess at the brand being GET
Under non-fault condition operations only, I assume you mean!No, because I don't routinely carry one on the van tbh, but, Ohms law stipulates that it couldn't pull any more than 39.25a anyway.
Under non-fault condition operations only, I assume you mean!
Under non-fault condition operations only, I assume you mean!
If your going to change the isolator, then change it for a Crabtree, they are about the best pull switches on the market and are rated at 50A not 45A....