I have a long running problem with the supply to a shower which has had my electrician tearing his hair out.
The shower is supplied through an MCB/RCD.
I had a simple switch (45A) which had been there for years and had serviced several showers without problem.
Then the switch started overheating. So the electrician came, thought it would be caused by loose connections and changed the switch. Same thing happened - this time he put a 50A switch in. Same thing happened again. This time we went for a contactor relay with a control switch. Now the MCB trips and can't be reset for a period.
So I got the shower company out (under the guarantee) to check the shower and they found nothing wrong.
Could the cable from MCB to the shower be damaged and would a damaged cable cause the symptoms described? Or what else could be wrong?
 
I have a long running problem with the supply to a shower which has had my electrician tearing his hair out.
The shower is supplied through an MCB/RCD.
I had a simple switch (45A) which had been there for years and had serviced several showers without problem.
Then the switch started overheating. So the electrician came, thought it would be caused by loose connections and changed the switch. Same thing happened - this time he put a 50A switch in. Same thing happened again. This time we went for a contactor relay with a control switch. Now the MCB trips and can't be reset for a period.
So I got the shower company out (under the guarantee) to check the shower and they found nothing wrong.
Could the cable from MCB to the shower be damaged and would a damaged cable cause the symptoms described? Or what else could be wrong?
Did your "Electrician" conduct any electrical testing, other than swapping parts willy nilly?
 
Your electrician can check to see if there is a fault with the cable and should have done by now.
 
a clamp meter on the feed in the CU would soon tell if there was excessive current. a continuity and IR test of the circuit would confirm whether or not the cable was damaged.
 
I agree with all the posts above. Get your electrician back or get a new one that can test it for you. Did you get any certs from your original electrician? like a minor works? It could have test results on it if he did them.
 
I agree with all the posts above. Get your electrician back or get a new one that can test it for you. Did you get any certs from your original electrician? like a minor works? It could have test results on it if he did them.
see that...... a pig just flew past.
 
Did he replace the cable that would of been subjected to thermal damage, by the previous loose connection, i.e. did he cut the damaged conductors back to undamaged cable?
 
He
I don't think he did any checks on the cable. How would he do this?
would/should have conducted tests using today's developments a MFT Multi function tester, IR, Continuity Zs etc, Get him back to do these tests, although from what you have said about his fault finding, doubt if he has such an animal.
 
Last edited:
I am getting a new electrician in - one that will do the investigative tests. Thanks for the advice.

When they send you a bill, please ask them for the details of the testing they have done ................

Paying for testing and not knowing what has been done isn't on in my "book"
 

Reply to Shower supply problem in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Replies
2
Views
711
Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
1K
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Hi, The shower pull chord switch has snapped at my mom’s home and having unscrewed the switch I discovered a horror show(see pic). So I’ve had...
Replies
39
Views
3K
Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock