riotmaster
I have a single phase power/ energy use monitor which is handy for checking how much power a company is using, when etc... very handy... you get the point.
However, as it is only single phase, assuming there is a balanced load across each phase, is it safe to say that if 2.37kW is the average reading for L1, the total of the three phases will be 2.37 x 3 = 7.11?
Not a trick question, just need to be sure I dont have to take any other factors or values into account...
Cheers in advance