I have not install site temps for a while so cant find in writing what i think is correct so please help if you can, as I need to have this info to insert into my test certificate.

I am sure that I remember reading somewhere that the site containers offices etc are not glassed as temporary as they do not move around and have fixed wiring from the supply so do not need to be checked every 3 months as lay down in the recommended testing periods for construction sites installations and the 3 month retest time only applies to circuits installed within the new building area IE (temporary sockets, lights, transformer, etc).

Am I correct in thinking this please ?
 
This always seems to be a unknown. All the retest times that are written are guides only as far as I know. The regs do say it is the installers decision on there knowledge of the installation to determine a suitable re-test period. Any written times from any books are only supposed to be there to guide your decision.
 
A lot of sites require testing 3monthly to satisfy their own H&S bods. Also insist on tools etc to be PAT 3monthly.
should say that this is for everything on site , cabins offices the lot.
 
After the initial EIC cert is issued after the set up. Which cert is to be used for the 3 monthly testing?
EICR, like any other periodical.
The aim is to find out if any faults have developed in the interim time period.

I’m sure the OPs case, it’s been tested a number of times in the 9 years since it was first posted
 

Reply to Site temporary re-testing time period question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, just looking for some advice about getting into site installation work. Currently 32 yo, 1.5 years qualified gold card in electrical...
Replies
9
Views
956
I will describe my problem in as much detail so you guys might be able to answer my question. I am never home, my Electric bill is $ 28 to $30 a...
Replies
23
Views
1K
Morning all, We are looking at qualification requirements for inspection and testing to BS EN 60204, all of our work is past the main isolator of...
Replies
2
Views
696
I have been tasked with seeing if a site is capable of accommodating a large new installation. I have done some working out but I'm not sure if...
Replies
7
Views
1K
Quite a few new builds are popping up locally in my area. I have noticed that they are not even being first fixed until the buildings are...
Replies
1
Views
816

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock