Discuss SMA 1200 Sunny boy not working in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

B

bigsparks

Hi

I have installed our first PV system, which we are using to get MCS accredited with. Its a small 5 panel system as roof space is quite small. The panels are 195w each.
The Voc for the panels @ STC is 45.21V and Isc @ STC 5.56A.
Our measured Voc on the day of commissioning was 211V. I thought this was reasonable as the Voc of array is 226.05V at STC. Our measured Isc on the day was 1.4A with an irradiance measurement of 270w/m2. Which when we adjusted figures to STC was nigh on perfect for the array. From these results we assume that the DC side of the install is performing as it should.
On our AC side at the inverter plug, we have 245V which is also the reading inside the inverter at the AC connections so I know that 245v AC is reaching the inverter.
However, the sma sunny boy 1200 is completely dead. No lights, no warning signs, no green flashing lights nothing. After triple checking our AC & DC tests again I thought that it must be a problem with th inverter. I got another exact model delivered and again nothing, no lights, no warning messages, completely dead.
Now ive tried getting hold of SMA technical in Germany as detailed on the manual but cant get to speak to anyone.
The min DC voltage input that the inverter needs at start up is 120V, so we are well within that tolerance. I wondered whether the 1200w inverter supplied was to big for the 975w array but the manual says that a green light should flash if the array is not prducung enough power to invert.
We had our MCS assessment yesterday, which we passed, but on the condition that they will need proof of the inverter working before we will get signed off.
Before I buy another inverter, ie a smaller mastervolt or the like, I wanted to see if anyone had any guidance or knowledge that 2 sparks and and mcs assessor could not see.
Any help appreciated.

Cheers
 
Haha!! You are RIGHT!! Many thanks, as they say you cant beat experience on what you are working on!! Im glad I came across this on our first install. Cheers once again.
 
In future, if you have the problem, disconnect the complete DC system and fire up the AC. That will then proove if the Inverter works. Bit concerned as part of your commissioning tests is array polarity.
 

Reply to SMA 1200 Sunny boy not working in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi everyone. The owner of the business I work for along with myself have created a DIY inverter setup that is giving us some issues. We bought...
Replies
4
Views
1K
Hi all, total newbie to the forum. I sincerely hope that those in the know-how would be able to assist me. On my semi-detached house we have an...
Replies
13
Views
2K
Hi there, I have noticed that my solar system has not shown any reading since December 18th. I have tried turning the system off and on but still...
Replies
23
Views
9K
Good evening all - I used to be a member of this forum ages ago, but couldn't work out what my username and old email address was, so decided it...
Replies
3
Views
4K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock