Doing a install for lighting specialist company,which involves Cat 7 cabling,quite a few to various points.
The engineer wants it put in the floor,before the actual floor goes down.
Seems a good idea but he’s on about 25mm plastic conduit,I’ve been looking at the plans,& I really dont think it’s a good idea.
There’s a lot of cabling,at least 4 Cat 7 to tv area plus co ax for TVs.
I’m more inclined to put 2x2 plastic trunking in,there will be no chance if renewing these cables,or putting loop or through boxes in,& no acess to it once the floor is down.
It’s the best route but not ideal,any thoughts on containment for this.
 
Just out of curiosity, what is the floor structure & thickness? Is it suitable to put 2" trunking in?
 
Sounds good advice,but he’s not really bothered about how or what we do,I’ve got ideas,just wondered what other thoughts would be.
 
Sounds good advice,but he’s not really bothered about how or what we do,I’ve got ideas,just wondered what other thoughts would be.
If he's not bothered, then do it the way you think is best,
 
How ironic a "smart home" install, installed stupidly, typical. Should not even be under the floor in the first place who thought that one up? What if UFH is wanted what will be the effect of that?
 
highlight your suggestions to the company /designer .
If they don't listen or change as you suggest and something happens in the future you have previously pointed it out.
Go with their specs as that's your contract. sometimes I find these specs can originate from the
Architect on drawings and they don't understand the full effects re other cables, or its their junior that's completed the drawings.
good luck
 
I have recently seen architects specifying 5 amp round pin socket outlets for standard lamps, you go into a shop and try and get a standard lamp with a 5 amp plug on it...
 
How ironic a "smart home" install, installed stupidly, typical. TShould not even be under the floor in the first place who thought that one up? What if UFH is wanted what will be the effect of that?
Yea, not really getting enough info,underfloor maybe the best option,there’s no real other way,it’s barn conversion,hiding cables are a nightmare,1st of power & lighting have already been installed,he’s suggested conduit in the floor,my concern would be accessibility after,but you could say the same about the other wiring & routes.
How ironic a "smart home" install, installed stupidly, typical. Should not even be under the floor in the first place who thought that one up? What if UFH is wanted what will be the effect of that?
 
I think the real problem I have or anticipate with underfloor conduit is the drag factor on pulling in at 3 or 4 or more cables. A couple of bends and you are in trouble I would say. Seems like you might have to deal with several bends usually anyway. Cauchemar!
 
25mm tubes with slight bends is fine but when you are getting to 90° fit adaptable boxes if you feel the pull is going to be difficult and placing stress on the cables.
 
Are all the data cables running back to one managed switch?

Or is it feasible to run one CAT to each point and use a smaller un-managed switch?
 
25mm tubes with slight bends is fine but when you are getting to 90° fit adaptable boxes if you feel the pull is going to be difficult and placing stress on the cables.
That’s my worry,it will not be possible without pull in boxes,but these will not be accessible after,obviously.
Thinking trunking.
 

Reply to Smart home install containment in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So what are your thoughts? Over 100 schools in England closed, 40 or so in Scotland after a building material with a projected lifespan of 30-40...
Replies
0
Views
451
I am a builder who is renovating a rural property. A smart meter is due to be installed. It would IMHO be a good idea to get a rec switch...
Replies
7
Views
1K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
I’m rewiring a massive house and there’s a feed to a c.u in the old black rubber cable that needs replacing. I know that Meter tails follow the...
Replies
12
Views
4K
Hi all, biting my tongue here! Have recently gone self employed in January, so cashflow is critical right now. I done some work for a lady...
Replies
36
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock