Discuss Smart light switch showing voltage when off in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
6
Hi - went to a client tonight to wire a two way lightwave smart master and slave switch. When connected as stated on instructions the light was permanently on and when the switch was actually pressed on the bulb flickered. When I checked voltage across the live and switch live terminals it showed as 50v when switch was off - any ideas what could be the issue? Thanks all
 
Check the bulb. If it's an LED, there may be compatibility issues.
You say you checked voltage between live and switch live?
Do you mean live to neutral, and sw live to neutral?

Also, double check the connections. The 3 terminals on both the master and slave are a live, a switched live and a signal between the 2.
This signal works on much less than 230v, so if you get the cables mixed up, and send 230v into this terminal, you'll fry the switch.
 
Hi - thanks for the reply

Sorry yes - l-n and s/l - n - the SW /L - N shows as 50v when switch is off?

I did ask him about the bulb as it was an LED one - he reckoned that lightwave said that was fine??

I used the spare L2 as the signal wire
The SW/L on its own and the L on its own as per instructions
 
I believe with the Lightwave products, they use a permeant feed through the switch, even when switched off, to operate the switch. In effect the lamp will still be receiving a supply when off to complete the circuit. Enough to operate the switch, but not enough to illuminate a lamp. Useful when you don't have a neutral at a switch, but you have to be selective with your lamps.

Think Lightwave have a list of compatible LED lamps because of that. You could check with them yourself.
 

Reply to Smart light switch showing voltage when off in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone :) my first post here. Quick background I'm a newly qualified installer of somewhat advanced years whose just starting out in the...
Replies
12
Views
1K
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
429
Hi all, I am upgrading my traditional 2 gang light switch in the kitchen to a smart 2 gang dimmer switch. When I wired up the switch the switch...
Replies
1
Views
1K
Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Replies
0
Views
610
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock