Hi there,
had a look through the other threads and couldn't find no answers.
So, here's the problem:
Fitted 20kwp with tripower1700 back in December.
Meter started turning backwards.
BG installed smart meter in Jan.(EDMI MK10D)
Had a look at the meter and noticed the Amps it's recording on each phase despite me not using much.
I decided to pull the fuses in order to disconnect all the consumers and left only the Tripower which wasn't generating on the grid.(late afternoon and overcast/display showed 0)
Result: 1Amp per phase (1A x 250V x 3Ph =0.75Kwh)
When I disconnected the Tripower from the grid the smart meter went down to zero!
I assume that if the meter is showing 1A per phase that it will be adding it to my total reading.
Has someone else come across this?
BG did reprogram the meter to include export, but it has not changed anything on my test results.
They say that they have never heard of this.
SMA in Germany are saying that they are experiencing a lot of problems with smart meters in Germany in regards with reactive power.
(I assume this might have to do with 3-phase, which is the common supply over there)
But they have not heard of the EDMI meter as G4S installed in my property.
Looking forward to receiving your responses!
Good day
had a look through the other threads and couldn't find no answers.
So, here's the problem:
Fitted 20kwp with tripower1700 back in December.
Meter started turning backwards.
BG installed smart meter in Jan.(EDMI MK10D)
Had a look at the meter and noticed the Amps it's recording on each phase despite me not using much.
I decided to pull the fuses in order to disconnect all the consumers and left only the Tripower which wasn't generating on the grid.(late afternoon and overcast/display showed 0)
Result: 1Amp per phase (1A x 250V x 3Ph =0.75Kwh)
When I disconnected the Tripower from the grid the smart meter went down to zero!
I assume that if the meter is showing 1A per phase that it will be adding it to my total reading.
Has someone else come across this?
BG did reprogram the meter to include export, but it has not changed anything on my test results.
They say that they have never heard of this.
SMA in Germany are saying that they are experiencing a lot of problems with smart meters in Germany in regards with reactive power.
(I assume this might have to do with 3-phase, which is the common supply over there)
But they have not heard of the EDMI meter as G4S installed in my property.
Looking forward to receiving your responses!
Good day