Discuss smoke alarms do i have to.. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

S

sivoodoo

Im wiring up a new extension to a house and am installing smoke and heats in the new extension.

Am I obliged to put interconected smokes in the rest of the house?

Thanks
Si
 
Yes, minimum of Grade D LD3 system to be installed when an extension is put up. The requirements for this sort of system is optical smoke alarms at top and base of staircases (escape route) interlinked with battery back up. Smokes at head of stairs must also be within 3m of bedroom doors.
 
Customer won't get there project signed off by the LABC without them. In other words they'll have to either like it or never be in a position to sell their house if they want to move on in the future. Best bet is to get the building inspector involved, i'm sure he/she'll put your customer straight.
 
Just looked it up in Electricians Guide to Fire Detection.

7.5m from habitable rooms. I must admit I thought it was 7 too.

I was going to run and get my book but I kinda thought you may beat me to it anyway lol

At least if I had have fitted them within 7m of habitable rooms then I would have been okay within the 7.5m ;)
 
I think that's 7.5m Dunc.

Within 7.5m of all habitable rooms, however a recommendation is made that there is an alarm fitted within 3m of all bedroom doors to provide sufficient sound levels to wake the occupants in an emergency. It's all to do with trying to ensure 75dB at the bed head of some or all of the rooms. If you look at this pdf document which is an overview of BS5839:pt6 it gives details of siting alarms with the 3m reference made in 'Alarm Sound Levels'.
 
Last edited:
Ask the BC to put that in writing incase of any problems in the future, cover your back mate, could save you time and money if the owners sell up in the forthcoming years.
 
Why on earth would someone NOT want smoke alarms in their home? I bet they wish they had agreed when they end up cremated in their own home lol

Dipsticks!!!!!! :(

I'm still trying to get my head around this one?

Who is signing the work off? If it's you then I would advise speaking with your scheme provider also :thumbsup
 
Get the customer to sign a disclaimer that you have advised your course of action and they are knowingly going against your professional advice
Put a sentance stating that they are liable for any addtional costs and legal come backs (such as home insurance not paying out)
 
Why on earth would someone NOT want smoke alarms in their home? I bet they wish they had agreed when they end up cremated in their own home lolDipsticks!!!!!! :(
I had this last week, I offered to install a heat and smoke detector whilst installing a house alarm. He said no, we have a battery smoke detector top of the stairs! Fare enough at least he has one but two hard wired into the alarm is much better.
 
This has came up with me and a few customers and i asked building control for southend area and basildon area in essex an they both said a small single storey extension doesnt warrant smokes but if its a double storey or loft extension then LD3 must be installaed as they wont sign off, i think in new build they must be to LD2 now
 

Reply to smoke alarms do i have to.. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
252
I currently have a home with 7 interconnected, hard-wired smoke detectors. I have a hard-wired heat alarm in the garage that I need to have...
Replies
4
Views
1K
I'm about to order this wired smoke alarm system as it can network but I just went to see how my existing fire alarms are hooked up and there...
Replies
12
Views
1K
Daughter has bought a house and it has a home security system, G-Tag setup. Issue is the alarm panel displays are pixelated and you cant see...
Replies
0
Views
629
I'm about to start first fixing this fire alarm in the industrial unit we are wiring, at the moment its totally empty and eventually will have a...
Replies
5
Views
828

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock