    Hi just a question, this morning I noticed a 2 gang socket had no power to it, went to check the fuse box/electric meter in the cupboard... and there was a lot of smoke coming out from somewhere? Its not smoking any more. The 2 way gang socket is completely dead. All other outlets seem fine and not affected.

    What would be the problem? Is this an expensive job, still waiting to here back from an electrician.

    Thanks
     
  2. Pete999
    Online

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    Needs sorting ASAP When did you notice the smoke, most likely a loose connection, advice switch OFF everything at the consumers unit (fuse box) and await the sparkie
     
    • Agree Agree x 6
  3. westward10
    Online

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Get someone in ASAP you could have a serious fire risk on your hands. Sounds like a poor connection which has overheated enough to burn the insulation. I would isolate it if possible.
     
    • Agree Agree x 6
  4. A14n
    Offline

    A14n Active EF Member

    Location:
    Norwich
    Everything from that socket is disconnected. I can't really turn off the power as I have a tropical aquarium. Still awaiting electrician... Noticed the smoke several hours ago now, nothing has happened since.
     
  5. Pete999
    Online

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    Up to you Mate but what would you rather have a burnt house or live Fish, a no Brainer in my mind switch the juice OFF. Can you smell dead fish no pun intended that's what an electrical fire smells like
     
    • Agree Agree x 4
    • Like Like x 1
  6. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    Edited :)
    The smoke is toxic, so get plenty of fresh air in. Switch off your isolator so you will be safe until the Electrician arrives.
     
    • Agree Agree x 2
  7. 7029 dave
    Offline

    7029 dave Trusted Advisor

    Location:
    bedfordshire
    As^^^ turn OFF immediately.
     
    • Agree Agree x 5
  8. onions1066
    Offline

    onions1066 Electrician's Arms

    Location:
    Nottingham
    Or be prepared and make some batter because if you don't turn off you might need it for the fish.
     
    • Funny Funny x 5
    • Agree Agree x 1
  9. marc8
    Offline

    marc8 Electrician's Arms

    Location:
    Essex
    Business Name:
    MTS Electrical Ltd
    don't use an electric fan to blow the smoke away use natural ventilation open windows
    best get some chips out also they go quite well
     
    • Agree Agree x 1
    • Funny Funny x 1
    • Winner Winner x 1
  10. Pete999
    Online

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    Not the last lot I had.
     
    • Agree Agree x 1
  11. davesparks
    Offline

    davesparks Trusted Advisor

    Location:
    guildford
    If you turn the power off your fish might die.
    If you don't turn the power off it could start a fire, in which your fish die and you loose all of your possessions and potentially could also be seriously injured along with the rest of your family.
     
    • Agree Agree x 3
  12. Murdoch
    Offline

    Murdoch Electrician's Arms

    Location:
    Woking
    Shame the OP hasn't updated us, despite viewing this thread a short while ago......
     
    • Agree Agree x 2
  13. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    could it be his smart meter having a crafty fag while the supplier is out for lunch, not monitoring said smart meter?
     
    • Funny Funny x 4
  14. Dave OCD
    Offline

    Dave OCD Electrician's Arms

    Location:
    Cornwall
    Business Name:
    Hendry Electrical Services
    It's the back up system when it loses internet connection, it reverts to sending smoke signals. :D
     
    • Funny Funny x 6
  15. A14n
    Offline

    A14n Active EF Member

    Location:
    Norwich
    Electrician is coming tomorrow morning now :/. Not had any issues so far since the smoke minus the dead sockets!

    I also have a landing light that hasn't worked for years, will get him to look at that also. Its on 2x light switches one upstairs and one at the bottom of the stairs... God knows what's wrong with that?
     
  16. Dave OCD
    Offline

    Dave OCD Electrician's Arms

    Location:
    Cornwall
    Business Name:
    Hendry Electrical Services
    That will probably be as simple as a loose connection in one of the switches, anyway your electrician will sort it out and restore your peace of mind hopefully. Let us know the outcome tomorrow.
     
    • Agree Agree x 5
  17. wirepuller
    Offline

    wirepuller Trusted Advisor

    Location:
    south uk
    Switch off for the night mate, not worth the risk. It's hardly going to drop below 15 degrees tonight, cant see your fish freezing, or run a lead from next door if that's possible.
     
    • Agree Agree x 3
  18. Gavin John Hyde
    Offline

    Gavin John Hyde Regular EF Member

    Location:
    Somerset
    As everybody has said turn it off, especially if you got children in the house. too great a risk.

    Would be nice if the OP returns and updates us. pictures of the offending article in the CU, if that is the cause would be good to see aswell.
    Wonder who fitted the CU and age of install? Surprised we don't hear of more problems like this to be honest, given the serious risks and the number of right shoddy and outright dangerous installs out there i am surprised there are not more house fires. as this was the premise on switching to metal clad CU's.... there is an awful lot of plastic ones out there still.
     
    • Disagree Disagree x 1
  19. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    plastic CUs don't cause fires. bad workmanship causes fires.
     
    • Agree Agree x 11
    • Like Like x 2
  20. 7029 dave
    Offline

    7029 dave Trusted Advisor

    Location:
    bedfordshire
    Absolutely agree he needs cut the electricity now.
     
    • Agree Agree x 1
  21. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    and maybe wrap a blanket round the fish tank. it's bye-byes time for fishes anyway.
     
    • Like Like x 1
  22. Gavin John Hyde
    Offline

    Gavin John Hyde Regular EF Member

    Location:
    Somerset
    The problem wasn't plastic Cu's as you said it was people doing a poor job and sometimes not tightening terminals correctly. I was taught on my very first job to use a tension screwdriver set to the right setting. My boss for a right one for the little details.
    By switching to metal i believe the idea was it would contain any fire better and give people a chance to notice and get out.
     
    • Agree Agree x 1
  23. D00DY_T00DY
    Offline

    D00DY_T00DY Gorilla Whisperer Electrician's Arms

    Location:
    UK
    Talking about this point to two joiners this morning "And what if the new metal cases become live like" "think the loose live would be more worrying then the CU being metal rather than plastic :D"

    Scapegoat for the poor workmanship of self proclaimed "electricians" :D
     
  24. A14n
    Offline

    A14n Active EF Member

    Location:
    Norwich
    Electrician had just been, our meter and fuse box etc etc is about 56 years old! and highly dangerous. There was an insulated cable in the back of the old fuse box totally melted and charred up. He's getting someone to fit a new system in and fix the light upstairs while he's at it.

    Damn that's soo bad.
     
    • Informative Informative x 1
  25. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    cheers for the update. the problem was either a poor connection or that particular cable has been overloaded.
     
    • Like Like x 1
  26. Specialist
    Offline

    Specialist Electrician's Arms

    Location:
    South Wales
    If the Fuse box & meter are that old and dangerous, what about the house wiring ? It's quite possibly well past it's use by date.
     
    • Agree Agree x 3
  27. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    agree. a rewire may be in order. an EICR would help.
     
    • Agree Agree x 3
  28. onions1066
    Offline

    onions1066 Electrician's Arms

    Location:
    Nottingham
    When I started there was no torque drivers I was told.........when your knuckles go white you know it's tight.
     
    • Agree Agree x 2
  29. A14n
    Offline

    A14n Active EF Member

    Location:
    Norwich
    Guy is coming about 6pm tonight now and staying until it's done. Charging £550... He didn't say about rewiring the whole house.
     
  30. onions1066
    Offline

    onions1066 Electrician's Arms

    Location:
    Nottingham
    This is a troll
     
  31. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    i'd imagine he'll be fitting a new CU.to latest regs. a full test of the house wiring is essential , as is dealing with any earthing and bonding issues. make sure you receive an installation certificate (EIC), and assurance of notification to building control. £550 seems about right for the above works.
     
    • Agree Agree x 3
    • Optimistic Optimistic x 1
  32. Specialist
    Offline

    Specialist Electrician's Arms

    Location:
    South Wales
    You really do need to get the wiring checked as well, odds on it's the same age as your fuse box.
    Only my opinion but I'd say 6.00pm is a rather unusual time to start a CU change out & then fault finding.
     
    • Agree Agree x 5
  33. A14n
    Offline

    A14n Active EF Member

    Location:
    Norwich
    Yes he did say we'll get a certificate. As couldn't sell the house the way it is.
     
  34. Spoon
    Offline

    Spoon Trusted Advisor

    Location:
    Lancashire
    But they just live under bridges... and don't need a CU....
     
    • Funny Funny x 1
  35. Andy78
    Offline

    Andy78 Trusted Advisor

    Location:
    Kingston upon Hull
    With any luck he'll have finished testing before he turns into a pumpkin.
     
    • Funny Funny x 2
    • Agree Agree x 1
  36. A14n
    Offline

    A14n Active EF Member

    Location:
    Norwich
    Photos of the ancient CU/meter.

    IMG_20170614_105016567.jpg

    IMG_20170614_105026024.jpg

    IMG_20170614_105043550.jpg
     
  37. onions1066
    Offline

    onions1066 Electrician's Arms

    Location:
    Nottingham
    Overhead line by the look of the way it enters. Can't see a main earth either but it could be the falling Greek sunshine affecting my eyes.......hope you lot are enjoying work lol. Makes the 6pm start even more impressive........
     
  38. A14n
    Offline

    A14n Active EF Member

    Location:
    Norwich
    Yeah it's an overhead power line. I finish work about 1am myself. Wonder if he will be finished by then? :)
     
  39. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    he'd better have a good battery floodlight then.
     
    • Agree Agree x 1
  40. Murdoch
    Offline

    Murdoch Electrician's Arms

    Location:
    Woking
    Most of those cables don't look too old...... wonder why the old CU wasn't changed?
     
    • Agree Agree x 3
  41. davesparks
    Offline

    davesparks Trusted Advisor

    Location:
    guildford
    That head looks pretty new, I'd guess the old overheads may have been replaced and a PME system put in their place.

    That fuseboard is a genuine antique, I don't think I've ever seen one made by the BI company before (later BICC)
     
  42. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    what's wrong with that ancient CU. it's metal, innit? :eek:
     
    • Funny Funny x 2
    • Like Like x 1
  43. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    bottom of bottom pic.are those forearm bones from the last sparks that attended?
     
    • Funny Funny x 4
  44. A14n
    Offline

    A14n Active EF Member

    Location:
    Norwich
    Yeah that's correct, he never made it... Talk about skeletons in the closet.
     
    • Funny Funny x 2
  45. Dave OCD
    Offline

    Dave OCD Electrician's Arms

    Location:
    Cornwall
    Business Name:
    Hendry Electrical Services
    It'll be interesting to see how he fits the new CU with the space available and length of cables etc. Honestly not a good idea to start this sort of job at 6pm though !
     
    • Agree Agree x 3
Loading...
Similar Threads - Smoke coming electric Forum Date
rcd tripping after smoke alarm fitted. Periodic Inspection Reporting & Certification Nov 13, 2017
smoke and heat alarm at the consumer unit Electrical Forum Nov 3, 2017

Share This Page

Users found this page by searching for:

  1. What does it mean when your electrical meter brings out smoke?

    ,
  2. electric meter got white smoke

  • Electricians Directory Post a Domestic Job Post a Commercial Job