Discuss Socket Zs High in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

AdieB

-
Reaction score
6
I have a supply in a log cabin, in the cabin is 6 double sockets and a couple of lights. Cables are in PVC conduit and are 2.5mm singles sockets and 1.5mm lights.

Sockets

L-L = 0.15 ohms
N-N = 0.15 ohms
E-E = 0.18 ohms
L1 with E2 & L2 with E1 = 0.07 ohms

L to E = >1000+ MG Ohms
N to E = >1000+ MG Ohms
L to N = >1000+ MG Ohms

Ze at board is 0.28 ohms 843 Amps.

Tested at socket Uc Rl 20 Amp 60898 type B

Socket 1 1.62 ohms 50V 0.04 V
Socket 2 1.29 ohms 50V 0.03 V
Socket 3 1.65 ohms 50V 0.05 V
Socket 4 1.62 ohms 50V 0.04 V
Socket 5 1.52 ohms 50V 0.04 V
Socket 6 2.12 ohms 50V 0.04 V Zs value to high.

This socket is approximately 300mm through a wall away from another socket. Only difference is that it is a waterproof socket with a neon indication. I have tried inserting the plug in and out numerous times in case of bad contact. I have taken the reading from the rear of the socket across the terminals and still the same problem. I am trying to come up with a reason for this.

Could change the mcb for 16A, but still can’t find the reason why it should be different than the others.

Any ideas?

Adie
 
take a reading at the outgoing side of the MCB. the difference between the reading you get and the Ze is internal res. of MCB.
 
Could it be due to tarnished connections on the outside socket ?

Is the outside socket part of the ring, or a spur ?

The other readings in your post look to be correct.
Sockets

L-L = 0.15 ohms
N-N = 0.15 ohms
E-E = 0.18 ohms
L1 with E2 & L2 with E1 = 0.07 ohms

Are you using the no trip setting (live test), or (R1+R2) (dead test) at the S/O's ?
 
i tend to disagree with the osg figures. why? because that 0.8 factor assumes that the cable will be loaded enough to run at it's rated operating temp. of 70deg. that situation, in a domestic environment is as rare as rocking horse poo.
 
I have a supply in a log cabin, in the cabin is 6 double sockets and a couple of lights. Cables are in PVC conduit and are 2.5mm singles sockets and 1.5mm lights.

Sockets

L-L = 0.15 ohms
N-N = 0.15 ohms
E-E = 0.18 ohms
L1 with E2 & L2 with E1 = 0.07 ohms

L to E = >1000+ MG Ohms
N to E = >1000+ MG Ohms
L to N = >1000+ MG Ohms

Ze at board is 0.28 ohms 843 Amps.

Tested at socket Uc Rl 20 Amp 60898 type B

Socket 1 1.62 ohms 50V 0.04 V
Socket 2 1.29 ohms 50V 0.03 V
Socket 3 1.65 ohms 50V 0.05 V
Socket 4 1.62 ohms 50V 0.04 V
Socket 5 1.52 ohms 50V 0.04 V
Socket 6 2.12 ohms 50V 0.04 V Zs value to high.

This socket is approximately 300mm through a wall away from another socket. Only difference is that it is a waterproof socket with a neon indication. I have tried inserting the plug in and out numerous times in case of bad contact. I have taken the reading from the rear of the socket across the terminals and still the same problem. I am trying to come up with a reason for this.

Could change the mcb for 16A, but still can’t find the reason why it should be different than the others.

Any ideas?

Adie

Are you getting this reading at each socket or is that just what you get at the connections at the DB??
 
Sorry tried to edit my last post but it did not appear.

The socket is part of the ring circuit. The cabling is exactly the same on all sockets. It is a TNC-s system, I pushed the plug of the tester in and out numerious times so hopefully no tarnished connections. I also took reading from rear of socket. The DB is a MCG fuseboard with a 2P6330 RCD and 2 x 60898 mcb’s 1x 20Amp 1 x 6Amp. What is the table or reg that says about rcd controlled socket can be 1667 ohms.
 
Am I missing something?

Shouldn't the reading be 0.35 (or even less with parallel paths) at all the sockets?


1666 ensures the RCD will disconnect before voltage rises above 50V.
It should not be used to ignore maximum Zs values - unless unavoidable (e.g. TT)
 
table 41.5, p50 in the red book. not sure where in bgb.
 
pushed the plug of the tester in and out numerious times so hopefully no tarnished connections

I meant where the cables terminate in the back of the SO too, as your end to end readings were ok.

What is the table or reg that says about rcd controlled socket can be 1667 ohms.

Table 41.5 (BGB) p57.

It actually says anything above 200 may be unstable wrt Earth rods.

Edit: Tel beat me to it, again! lol
 
Last edited:
the 1667Ω figure is for earth faults, and not for live-n faults. I would carry out a Zp-n, which means that you test between live and neutral, not live and earth. If your using a fluke, its just a case of swapping the leads over, but if its a megger, then youll have to use the probes. If this comes up ok, then youve identified that it is indeed a problem with the earth path, and not the live. If it comes up bad, then it means that you have problems wiuth either your live or neutral.
 

Reply to Socket Zs High in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello, looking for some advice on 2 things please. Ive tested a ring main in a house with RCD protection, the results ive had are L-L .43 N-N...
Replies
24
Views
5K
carried out dead testing on new site accommodation,all dead tests were fine however, when I conducted live testing I got high zs redings on...
Replies
16
Views
3K
Hi all, Doing some pre board change testing and ive found 2 sockets with high Zs readings. Everything else is fine, done all my end to ends and...
Replies
53
Views
5K
This has messed my head up so much I’m not sure I can even explain it properly but hopefully someone out there may give me ideas of what to do...
Replies
30
Views
10K
Hi, I was wondering if you guys can help with some errant test results. I'm testing a ring and i get L-L = 0.41 N-N = 0.40 E-E = 0.63 Great...
Replies
16
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock