Yorkie14

Hi we noticed our solar must have fused and tripped out the consumer unit for most of September which is really annoying - all that sun! we reset and now it has done it 3 times over this week. What could be the cause? we have never had any problems. We live in Swindon but the installation was done by a Taunton company. Photo of set up attached. Would appreciate some ideas of what to do probably out of warranty...

IMG_3035.JPG
 
not into solar, but my first suspect would be the inverter. is it tripping a MCB or a RCD? check out out electricians directory and find one who does solar close to you. a short visit to ascertain the problem is not expensive.
 
If the RCD is tripping ( this protection device has a test button on it) then it could just be a case of changing it for a RCD that has a higher mA tolerance. 30MA can nuisance trip a lot on solar PV inverters. If an MCB is tripping it would be a good bet it is an internal fault in the inverter. What inverter do you have?
 

Reply to Solar system 5 years old suddenly tripping consumer unit in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello there I have just installed a new Solis S6-GR1P3.6K-M-DC Inverter - this replaced a 10 year old+ Sungrow inverter that failed/out of...
Replies
5
Views
2K
I had a PV system installed by a local reputable manufacturer last autumn; since then, I've received conflicting advice regarding the consumer...
Replies
2
Views
2K
Hi all, My 3 month old grid tie inverter has tripped on 3 occasions at startup. Have read plenty of threads here about similar issues but unclear...
Replies
1
Views
2K
Hello All Can I say to start with I am not an electrician but used to be a heating engineer (yes I can hear the groans). I have wired the...
Replies
85
Views
14K
I try to keep out of Domestic work but I have a problem at home. Currently I have a wylex fuse board with re-wire fuses. they are great because...
Replies
55
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock