Smudge

just a quick one...a job we are downing includes installing downlighters along a corridor of a house. The void is only 90mm. I want to use fire rated 240V downlights, but before buying (from the internet) a lot of the shallower ones i'm looking at doesn't specify a clearance dimension around the fitting. Most do, ie/ 100mm, 50mm, 60mm etc etc. Is this distance determined by the manufacturer? or is there a set standard for this?
 
Clearance around the fitting is usually included in the instructions, but is about 50mm to allow the fitting to 'breath' , heat to dissipate (this also includes at least 25mm above the fitting). Otherwise you end up with shortened lamp life. It is rare to get a FRD (Fire Rated Downlight) with a recess height of less than 100mm.
 
i'd say a minimum of 4" all round as regards insulation. you can be closer than that to a joist, say 2".
 
so how tall are the fittings you are considering using?
 
Wouldn't have thought that a legitimate piece of equipment (one conforming to a british or european standard) couldn't not contain this info. Copies / lookalikes maybe but the absence of any certification would ring alarm bells with me.
 
in this situation i would use bell non fire rated fittings, only about 50mm tall,as long as the floor above was not separately occupied, and seriously consider LEDs. or, even better, use the sealed unit LED fittings, then nobody can fit halogens.
 
Last edited:
Wouldn't have thought that a legitimate piece of equipment (one conforming to a british or european standard) couldn't not contain this info. Copies / lookalikes maybe but the absence of any certification would ring alarm bells with me.

You cannot access all safety specs for lights online. ie/ clicks fire rated downlighters give the dimensions but not the clearance space, as do many others. When i tried phoning our usual wholesalers, they didn't know as they, like most wholesalers are railroaded into certain products.

i seen some 50mm ones, but the customer didnt like them. They have now chose the lights themselves which are 100mm deep. The only way round it now would be to remove the deafening boards above each light. It's all one property, so it's not affecting anyone elses living.

I have never had to go to such extremes before, is this a common practice?! and more importantly, is this allowed?!
 
i always do, just for a better piece of mind. Prob just a personal thing. Same as bathrooms, i always fit shower rated even if its outside zones. Just the way i've always done it.
 
Fare enough smudge can't argue with that. On this occasion you may have to use the less bulky none rated fittings if you can't find the right size fitting, at least you have the option.
 
he ain't now. customer has bought the fittings. B&Q strikes again.
 
or, dare we mention lightcraft. lights from £9999 to £1. as advertised on the radio station
 

Reply to space around fire rated downlighters? in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Similar Threads

Evening, Feeling really confused about fire rated downlighters. We need 26 for our extension which is part flat ceiling and part vaulted ceiling...
Replies
30
Views
4K
Am hoping you can help Following an integral garage conversion, I am after a couple of fire hoods to cover some LED ceiling spotlights. The...
Replies
21
Views
2K
Doing an EICR today, in a multi occupied house, I was chatting to the landlord advising him to get fire rated downlights in the celar bedroom...
Replies
14
Views
9K
Squid
S
I'm a bit confused about using the bit of white heat resistant flex for downlights. Do we really need it on fire rated downlights? Isn't it just...
Replies
11
Views
3K
Why do people still make none fire rated down-lights? Got to do a quote for a new build where the client wants fittings that are not fire rated...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock