Discuss Split Concentric Termination in the UK Electrical Forum area at ElectriciansForums.net

catdog

-
Reaction score
13
I'm no expert on split concentric (assuming that's what this is)......But an earth clamp doesn't seem the best solution to this (also as the earth cores appear to be insulated!

This is for an eicr on a sub main but I'll have to do the remedial work at some stage.

Any advice on how to terminate this correctly?

Thanks!

1546696944971564378322765861338.jpg
 
That is concentric but not sure that clamp serves any purpose unless the insulation below it has been removed.
 
Nope doesn't look like it has been! I was just doing an initial check today but the sockets this isolator supplies are earthed buy must be via another means!!
 
That looks like the neutral part of the concentric cable exposed , sorry never terminated that my self but i agree with you thats certainly not the way to terminate any CPC
 
If that is split concentric which it probably is the outer neutral conductors should not be connected to earth, assuming this is the consumers installation.
 
If you have no slack on the cable you have a problem as those neutral conductors should be correctly enclosed.
 
Is there a gland specifically for split concentric then?
No you can either not gland provided it is correctly supported or put a stuffing gland in place. It is no different to terminating a standard cable but the cores have a different configuration. Have you not looked inside the switch-fuse.
 
Have you looked inside the switch normaly all the black are terminated into the neutral and the greens terminated into the earth , just wondering how the earth is terminated inside
Edit just seen westwards post , he beet me to it
 
Haven't looked inside yet! This was one of many issues found when fiing out paper work and before removing any covers! When I get back to it I'll send a pic of inside (partly don't want to open it!)

Thanks for reponses
 
The current version of BS951 prohibits the use of such a clamp in this manner.
If the cable is buried then unless it has suitable additional mechanical protection then it is not in accordance with BS7671.
 
Not aware of any requirement in BS7671 to provide mechanical protection to cables buried in the ground?
NBP is presumably referring to 522.8.10 where cables without an incorporated, cpc suitable, earthed covering should be protected against mechanical damage by a conduit or duct.
Even though the regulation is worded with reverse emphasis.
 
I agree, concentric is live centre conductor and pen outside conductor. Split concentric is live centre and split outer earth and neutral separate, not seen it with swa but that's not to say it doesn't exist!
 
Originally concentric cables were deemed okay in walls without additional rcd protection but this was later removed.
 

Reply to Split Concentric Termination in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Did an EICR that passed 5 years ago Several things in the picture raised concerns for me. Comments please - photo at end First photo shows a...
Replies
9
Views
1K
Hi I've inherited a very tight space, a KMF switch and some split-con for a sub-main to try and tidy up. It's a joyous non-restrained single...
Replies
3
Views
134
I recently purchased a rural property in Arizona. The property receives power from APS, the local electric utility. Power arrives from the...
Replies
3
Views
801
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
652
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock