Discuss Spur from ring final circuit into shed 2 way DB in the Australia area at ElectriciansForums.net

P

Paul Downham

Hi all,

I need to run power to a shed but access to the main indorr DB is very awkward. I plan to do the following but would welcome your comments;

The customer requires the following;


  • Power to a 2 way board in the shed
  • Power from the shed 2 way board to an IP66 FS (5A) for a pond pump
  • power from the pond pump IP66 FS to another IP66 FS (5A) for garden lighting at some point in the future
I plan to;


  • Run a cable from the GF ring in 2.5 t&e to outside and terminate in an IP66 13A FS mounted on the external rear wall
  • Run 2.5 SWA from the IP66 13A FS to the shed
  • Mount a 2 way board in the shed (has 16A and 6A MCB's) and a 30Ma RCD
  • Earth spike from board (TT system) in 10mm CPC
  • Run 2.5 SWA from DB 16A MCB to IP66 5A FS for pond pump
  • Run 2.5 SWA from IP66 5A FS pond pump supply side to next IP66 5A FS and terminate
I would welcome your comments as I am unsure about 13A FS to another DB. I have read the following but this doesn't cater for this situation http://electrical.------.org/wiring-...6/complete.cfm

Many thanks

Paul
 
i would seriously rethink access to the CU.
 
Why put in another db, if you are coming off the ring, presumably 32A Rcd protected, then a fcu feeding two more FCU's would be OK. The problem lies with the RCD, any faults in the shed/pump/lts will trip the ring RCD in the house whether you put another RCD in the shed or not.
 
Thanks guys. Comments noted.

Have asked the customer if a 2 way board is required.

If not, I will spur from GF ring into 13A FS and go straight to pond pump 5A spur and onto further point 5A spur.
 

Reply to Spur from ring final circuit into shed 2 way DB in the Australia area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
L
So my old man is planning on setting up a fish shed which will hold 2-3 fish tanks. The power drawn from the equipment which will be running in...
Replies
15
Views
2K
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
611
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
I’m a trainee electrician and would really appreciate the benefit of someone’s skill and experience on the following: Our house is a TN-C-S (100A...
Replies
70
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock