UK Spur off a 4mm twin and earth, 32amp radial

Discuss Spur off a 4mm twin and earth, 32amp radial in the UK Electrical Forum area at ElectriciansForums.net

JLH520

DIY
Reaction score
0
I have a dedicated radial from the consumer unit to my conservatory. This was installed using 4mm twin and earth as it gives the option to use multiple electric heaters on a 32amp breaker if needed. The circuit consists 4 double sockets plus one single socket on the end, in a weatherproofed box on the wall outside. As it happens, I rarely need to use electric heaters in there, as there are plumbed radiators too, so the radial is easily over specced and currently has only a 16amp breaker.

Now I need to add two extra double sockets outside to power two 2500 watt infra red heaters under a gazebo (each has a 13 amp 3 pin UK plug fitted, they won’t be hardwired). I am hoping to be able to add these sockets by running a spur from the conservatory radial circuit as it could comfortably cope with the draw from the heaters. My intention was to continue a 4mm twin and earth spur to these additional two sockets outside so that the whole radial is safely capable of handling 32 amps.

The problem is that a fused connection unit which handles a fuse above 13 amp doesn’t seem to exist, so I’m wondering how best to safely connect this spur to my radial circuit and isolate the outside circuits if need be?

Any helpful suggestions on how to implement this would be greatly appreciated
 
75?

You’ll be looking forward to a life of diddy little diy jobs, watching YouTube videos of tractors, engines and other machinery just moving…. Not actually doing anything and drinking copious amounts of coffee…

That’s what my 75 year old dad does

Sounds OK to me that! Swap coffee for beer though.
 
even though, eack kWH will dry to a set level. 5kW will just be quicker then a 3 kW unit. energy in = energy out, and all that.
MUCH quicker than a UK domestic drier. It uses moisture sensors and 'fuzzy logic' to keep the electricity consumption to a minimum for a non heat pump drier, but I still see £ signs in front of my eyes when I watch that meter light flashing.
 
Thank you all for (A) putting me straight on a couple of points, and (B) providing the answers I was looking for.

To clarify a couple of points - yes the circuit is, and will continue to be RCD protected and I will extend onto the end of the radial, rather than cutting in between the existing sockets (not sure if that would change anything.)

I will also change the circuit MCB to a 32 amp to cope with the heaters.

Thanks again.
And then you will use a multifunction tester and do a r1 r2 test, a Zs test, a RCD trip time test and complete a Minor works cert,,,,Wont you
 
IT is a

There is a recommendation that loads of 2Kw and above need to be on their own dedicated circuit, not fed via a 13 A spur
Normally hard wired, yes, but it says heater has a 13 amp plug top, Which is man fact fitted, i dont agree that a 2.5 or 3kw heater especially outside should be on a plug top, as we all know , seperate supply For these they could be on for hours.
 

Reply to Spur off a 4mm twin and earth, 32amp radial in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top