Discuss Spuring off a ring main in the The Welcome Forum area at ElectriciansForums.net

Robbo

-
Reaction score
1
Hi.

New to site. After abit of advice.

Adding a 13 amp fused switched spur to a ring in 2.5 mm t&e, only the current wiring is in 2.5mm with 2.5mm cpc. Protected by a C32 RCBO 30mA , only the CPC is going to be mixed 1.5 and 2.5.
Can’t fined anything in regs book about mixing cpc. Any advice would be great.
 
As long as the CPC satisfies the adiabatic for your addition then no problems.

Is the existing ring run using singles in conduit?
 
Thanks guys.

Yes thought about using singles. Not often I come across this situation. Didn’t want to spend on cable I’ll never really use to be honest. It’s only for a supply for a StairLift charger in a sheltered accommodation.

Normally only do Domestic. 2.5mm t&e all time.
 
Long time since I done any singles stuff; but wasn't just easier to order three drums of 2.5mm.
If you are concerned about changing the cpc size order 2.5 brown and blue and 1.5 0r 1mm depending on what size the cpc is in the twe
 

Reply to Spuring off a ring main in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I am sure when I qualified for the 16 edition we spoke about how to treat a ring main. I know the majority of the time we just learned how to read...
Replies
178
Views
14K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
592
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...
Replies
4
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock