Hi All

Could someone explain this to me please. Connected to the contactor, over load are two coils (are they ferrite chokes) please see photos. Also why only two and not three one for each phase, marked with a 65 in the photos.

The motor is used to control a blower unit, that moves a bean crust/shell through a plastic pipe to a collection bag.

Any help you can give me, really would appreciate it.DSC_0150.jpg DSC_0154.jpg DSC_0155.jpg DSC_0155.jpg DSC_0156.jpg

Cheers All, thanks for reading.
 
I think the two devices are current transformers which are measuring the currents in two of the three lines feeding the motor. One can see thin red and blue wires coming out of the device as well as the two thick black conductors. Since the motor is a 3 wire balanced load the two wattmeter method (Blondel's Theorem) can be used to measure the instantaneous power being drawn by the motor. Elsewhere line voltages are measured (or assumed).

These two lines' currents and their corresponding line voltages with respect to the common unmetered line are input to a wattmeter to indicate power. See Figure 4 of :

Three Phase Power Measurement in Three Phase Circuits - Electrical Academia - http://electricalacademia.com/electric-power/three-phase-power-measurement-three-phase-circuits/

See also Blondel's Theorem:

https://wikivisually.com/wiki/Blondel's_theorem
 
Last edited:
Re: westward10's #3:

And the reason why there are only two saturable reactors is because the thermal overload module is a two heater elements type? ie: it only has heaters in two lines, the third line being a solid connetion between in and out. The two saturable reactors are wired in parallel with these heaters.

And the red and blue wires I thought entered the SRs do not - I need to go to Specsavers.
 
Hi All

Could someone explain this to me please. Connected to the contactor, over load are two coils (are they ferrite chokes) please see photos. Also why only two and not three one for each phase, marked with a 65 in the photos.

The motor is used to control a blower unit, that moves a bean crust/shell through a plastic pipe to a collection bag.

Any help you can give me, really would appreciate it.View attachment 48190 View attachment 48191 View attachment 48192 View attachment 48192 View attachment 48193

Cheers All, thanks for reading.
CTs for metering purposes maybe
 
Last edited:
Re #9 Ironbones: You know a motor draws more current on start up than when running normally. You also know a thermal overload relay detects overload by the Ohmic heating (I2R) of bimetallic heater elements. For a motor which starts 'quickly' the rise in temperature is not enough to trip. For a motor which starts 'slowly' there is a prolonged period of Ohmic heating of the heater elements which could cause the relay to trip which would be a nuisance. When the motor is running normally one wants the overload trips to ignore short term overcurrents but respond to sustained overcurrents. So how to ignore the initial surge current? One answer is a saturable reactor(inductor) which shunts the heater element. A saturable reactor's inductance and hence reactance depends on the current flowing through it - the higher the current the lower the inductance and hence its reactance. So, during the start up when the surge current is high the saturable reactance shunts the current to flow through it more than through the heater element.

Simply put at high currents, the magnetic dipoles in the metal of reactor/inductor's former are all aligned which means any further increase in magnetising force (ie:Amp turns) (due to an increase in motor current) causes no further (or much reduced) increase in magnetic flux - saturation. The effective inductance and hence reactance thus reduces to a small value and the current through it 'only' has to contend with the resistance of the winding - which is low. Careful selection of materials for the former and number of turns around it ensures that the onset of this reduction in reactance occurs for currents beyond the upper end of the operating current range of the thermal part of the relay.

A saturable reactor is an example of a non-linear passive component; its electrical properties, in this case inductance does change with the current through it. All chokes, transformers, motors can/do saturate if the current is high enough.

Others can polish up this explanation.

permeability-and-saturation-2.jpg
 
I found this image of a Mitsubishi thermal motor overload relay with saturable reactors:

MITSUBISHI ELECTRIC Global website - http://www.mitsubishielectric.com/fa/id_en/products/lv_distri/lv-switchgears/overload-relays/index.html#pageUnit03

Such a blower as mentioned by the the OP perhaps has a long run up period which requires this type of O/L protection device to avoid nuisance trips during start up.

Marconi, thanks for your explanation its greatly appreciated.
 
The purpose of a thermal overload relay is to detect long, low level overcurrents that would overheat a motor winding. In a perfect world, the relay would track the temperature of the winding closely (as more sophisticated electronic protection does) responding only when the winding is at risk. Although more sluggish than a fuse, the heater box still has a lower thermal time-constant than that of the motor, due to a lower mass. When presented with a short, higher overload situation such as a start against a high-inertia load, the adiabatic surge of heat input may cause the overload relay to trip while the motor is still nearly cold.

Under these conditions, the voltage across the heaters is sufficient to drive enough current through the reactor to saturate it, diverting some current away from it and reducing the relay's short-term sensitivity. The time / current curve of the overload relay is therefore modified by the non-linear response of the reactor. The heaters will still be heated to tripping point, but not by a heat input proportional to the square of the line current as would otherwise occur.

An alternative approach used in older gear was the hydraulically damped magnetic overload, which had a non-linear response. Allen-West were very partial to a hydraulic dashpot or three, as anyone who has ever had a case of A-W starters overturn in the back of the van will know.
 
Somewhere amongst my junk I have one of the old glass bottles which came with the Allen-West starters still with its oil and cork stopper. The dash pots had a disc in them with varying size holes which was spun around to adjust the dampening.
 

Reply to Still Learning -Whats this for connected to contactor and overload. in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

A bit of a mini essay but these questions have been building up in my mind over the last weeks and months as I've been studying and volunteering...
Replies
6
Views
3K
We have this Swiss-made Dixi horizontal borer from 1957, very nice machine still with its original DC variable voltage drive. In those days there...
Replies
9
Views
2K
I'm looking at a German made roller conveyor system 10 motors contactors controlled by a PLC Issue is customer says 3 mths ago motors started...
Replies
23
Views
3K
About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K
....TN-S appears outside, butt TT employed inside. Good Evening Everybody (This is my first post) Overview: The supply to my parent's cottage...
Replies
29
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock