Hi , I know this has been covered before but i'm still unsure and concerned about nuisance RCD tripping after replacing a consumer unit if there are borrowed neutrals , especially on the lighting circuits.

Last time i posted regarding this I was left confused as there were many different ideas and suggestions about how to test for this but no definite 'this is what you do'.

Can anyone explain to me exactly what to test for and how to do it to prevent problems after fitting a new CU.

Any help with this is much appreciated.:)

Chris.
 
Continuity and/or IR test between neutral conductors.

If no reading on continuity or a infinate reading on IR then they is no connection between the two.
 
OK first things first if you give the old CU a Ze-PFC-IR tests and everything is good to go count the lives and the neutrals at the board and it should be the same ie 12 reds 11 blacks pay attention to the cable sizes ie 10,6,4,2.5mm should be paired up but you may find 2 x 1,1.5mm reds and 1 x 1,1.5mm blacks
 
On domestic, its about checking for continuity between neutrals on radial fed circuits. Continuity would point towards borrowed neutrals. But remember to have the loads switched on ie lighting circuits bulbs in switches on, if you get my drift. Remember ring mains will have continuity anyway, at least they should. Most problems are with the landing light on the 2 way. The quick answer is to put both circuits on the same rcd but seperate breakers many do this.:D

Officially rewire the landing light with the downstairs circuit.;)
 
But what if the lighting circuit is wired in the three plate method from what i can workout you would have to make sure all the switches were on and all the lamps were good otherwise a blown lamp or open switch could indicate that everything was ok but still you could have a borrowed neutral - does that make sense ?

Thanks

Chris :)
 
Baldsparkie , you got in there just before me as i was typing !

Thanks for your help , i understand what you say about switches on , bulbs in , that in fact was my question so you've already answered it.

Two other questions - Is it ok to insulation resistance test with the switches closed and lamps in ? Also what if you have lighting transformers e.t.c. surely they'll give false results.

Also you say put both circuits on same RCD but different breaker but I thought that was not allowed because if RCD trips you lose all lights ?

Thanks again for your help :)

Chris
 
On domestic, its about checking for continuity between neutrals on radial fed circuits. Continuity would point towards borrowed neutrals. But remember to have the loads switched on ie lighting circuits bulbs in switches on, if you get my drift. Remember ring mains will have continuity anyway, at least they should. Most problems are with the landing light on the 2 way. The quick answer is to put both circuits on the same rcd but seperate breakers many do this.:D

Officially rewire the landing light with the downstairs circuit.;)


I'm sure its not just me who would mention this, but shouldn't you put both lighting circuits into the SAME MCB if they have a borrowed neutral?!?!
 
I'm sure its not just me who would mention this, but shouldn't you put both lighting circuits into the SAME MCB if they have a borrowed neutral?!?!

Ask yourself this A wylex rewirable board has 2 5amp circuits. They have been in service for 25 years and despite having a borrowed neutral for the landing light, the occupier has never had a problem. By all means you can go for one breaker. But if your going down the good electrical practice route, then its a landing light re wire.;)
 
Baldsparkie , you got in there just before me as i was typing !

Thanks for your help , i understand what you say about switches on , bulbs in , that in fact was my question so you've already answered it.

Two other questions - Is it ok to insulation resistance test with the switches closed and lamps in ? Also what if you have lighting transformers e.t.c. surely they'll give false results.

Also you say put both circuits on same RCD but different breaker but I thought that was not allowed because if RCD trips you lose all lights ?

Thanks again for your help :)

Chris

Is it ok to insulation resistance test with the switches closed and lamps in ? Not really you answered your own question with the bit about trannies. Any resistive load between lives and neutrals will mess your insulation readings.

I thought that was not allowed because if RCD trips you lose all lights ? True, but if your downstairs and the upstairs lights are still on they wont help much anyway.
In the real world its more usefull to keep power circuits on different rcds.

Hope the above helps Chris ;)

 
Ask yourself this A wylex rewirable board has 2 5amp circuits. They have been in service for 25 years and despite having a borrowed neutral for the landing light, the occupier has never had a problem.

If there is a borrowed neutral then supplying this through two separate MCBs renders those circuits DANGEROUS. They must be one circuit.
 
If there is a borrowed neutral then supplying this through two separate MCBs renders those circuits DANGEROUS. They must be one circuit.

So give a situation that would render this dangerous to the house owner.
Are we saying the original circuits have been dangerous since completion of the install 25 to 30 years ago and whilst connected to the original c/u. :);) Thats a long time and a lot of use, there are a lot of very lucky home owners, if as you say its dangerous. (I know where your coming from but think about it)
 
@baldsparkies. The situation is dangerous when say you change an upstairs light for the customer in the bedroom for example. You turn off the upstairs MCB and then test for voltage. As youd expect thered be no voltage and you then begin to carry out the work. Once you have disconnected the core and seperated them, someone accidently turns on the 2 way switch for the landing light. One of the neutrals in your separated cables is now live and ready for you to touch =) that is why it is dangerous.
Live supply is linked from downstairs light and then travels to upstairs light, obviously if the switch is in the on position this will send a live supply through the lamp, down the neutral which you may have disconnected making it live.
 
@baldsparkies. The situation is dangerous when say you change an upstairs light for the customer in the bedroom for example. You turn off the upstairs MCB and then test for voltage. As youd expect thered be no voltage and you then begin to carry out the work. Once you have disconnected the core and seperated them, someone accidently turns on the 2 way switch for the landing light. One of the neutrals in your separated cables is now live and ready for you to touch =) that is why it is dangerous.
Live supply is linked from downstairs light and then travels to upstairs light, obviously if the switch is in the on position this will send a live supply through the lamp, down the neutral which you may have disconnected making it live.

I completely agree with you. The situation you describe is far from ideal.
The real answer, if your customer won't agree to re wiring the lighting circuit is to put both circuits with the shared nuetrals into one mcb.
That way it would be a departure from the regs at code 4 rather than a borrowed neutral situ code 2.
I can't remember the last time a borrowed neutral ambushed me. Or even what profanities I used to make others aware of my lack of approval.
As a competant person, you should never assume, cus it makes an --- out of U and ME.
With domestic installs its easy to cover yourself ie check in advance identify and isolate as neccassary.
The borrowed nuetrals are out there right or wrong, sparky beware. If not you will learn, the hard way. Not a good answer I admit, but its a real world answer as many on the forum will confirm.
Oh yes it was an emergency lighting circuit in an office block, back in the 80s I believe. Thats the last one that got me.
Anyways, with all these people raving about rcd's you will only get a tingle if that. (Im such a bad lad, what a wind up merchant)
One other point, Non competant persons should not be touching the installation.
You are the sparky working on the lighting circuits, you are the sparky disconnecting the nuetrals, and to be fair you are the sparky who created the situation. It was safe before you started tampering, sorry but true.
 
Last edited by a moderator:
In 36 years in Scotland I have never come across a shared neutral or have I lived a sheltered life ?

Hate to say it Old timer, but maybe Scottish sparkies are better than us English boys.:eek: Either that, or your a lucky old bu##er.:D
Listen to me mate, talk about pot calling the kettle black;)
 
I completely agree with you. The situation you describe is far from ideal.
The real answer, if your customer won't agree to re wiring the lighting circuit is to put both circuits with the shared nuetrals into one mcb.
That way it would be a departure from the regs at code 4 rather than a borrowed neutral situ code 2.
I can't remember the last time a borrowed neutral ambushed me. Or even what profanities I used to make others aware of my lack of approval.
As a competant person, you should never assume, cus it makes an --- out of U and ME.
With domestic installs its easy to cover yourself ie check in advance identify and isolate as neccassary.
The borrowed nuetrals are out there right or wrong, sparky beware. If not you will learn, the hard way. Not a good answer I admit, but its a real world answer as many on the forum will confirm.
Oh yes it was an emergency lighting circuit in an office block, back in the 80s I believe. Thats the last one that got me.
Anyways, with all these people raving about rcd's you will only get a tingle if that. (Im such a bad lad, what a wind up merchant)
One other point, Non competant persons should not be touching the installation.
You are the sparky working on the lighting circuits, you are the sparky disconnecting the nuetrals, and to be fair you are the sparky who created the situation. It was safe before you started tampering, sorry but true.

But this should only be done if both circuits were originally on MCBs of the same rating. E.g. if an upstairs lighting circuit (6A) has borrowed a neutral from a downstairs ring (32A), then it is not advisable to put both circuits on the same MCB (presumably 32A) because there is not enough overcurrent protection for the upstairs lighting circuit (most likely installed in 1mm2 or 1.5mm2 T&E). A design exercise should be carried out before this is done and if it's not pretty some additional wiring is the best way. However, for the benefit of this scenario, would anyone consider putting an appropriately rated FCU in line adjacent to the CU for the lighting circuit therefore allowing both circuits to go on the higher rated MCB?
 

Reply to Still unsure about testing for borrowed neutrals. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

During some testing I found a N-E IR fault on the kitchen lights of 0.1Mohms. I also found a N-E IR fault on the ring sockets, again 0.1Mohms...
Replies
58
Views
8K
Hi everyone, I want to repurpose an old cable that was previously used to power a 3-phase machine. The cable is 4L1.5 micc, and I don't want to...
Replies
7
Views
1K
Evening all, I had a quick Friday afternoon domestic job that has turned into a PITA and I'd appreciate your help. While adding some new lights...
Replies
10
Views
838
Evening all. I did an EICR recently and then changed a consumer unit. As part of the EICR process I take off around 25% of all accessories to...
Replies
9
Views
2K
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock