Discuss Stramit - Straw Walls - Installation Reference Method in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
116
Evening all. Working on a bungalow at the minute with the dreaded stramit walls.

All my new cables have been surface, galv capped and the builder is dot 'n' dabbing over. There is an existing radial serving sockets in the living room which is not being rewired. For those that are familiar with stramit, cables are fed through channels in the wallboard either up or down to the loft or floor void.

Do I class cables fed in these channels as reference method 103? If so this would make a 2.5mm radial rated at 13.5A. If that is the case what MCB do I put on that? Doesn't work does it?
 
Last edited:
Hi - just having a read about this type of construction, so def not expert. My thoughts are : if it's an early type with vertical chases into the compressed straw then I agree with your 103 thought and 10A is all :( .
Depending on exact building method it might be 102 (where is cable in the chase, how is chase filled) and then 16A or 20A may be ok.
Can the 2.5mm be replaced with 4mm? Or surface mounted?
 
No it is in the channel, surrounded by compressed straw. I may be able to get a leg back from the last socket to form a ring but its not going to be easy. Don't think i've got an option.
 

Reply to Stramit - Straw Walls - Installation Reference Method in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone. I need a little advice please. Several months ago I first fixed and second fixed a timber frame loft conversion ( open plan living...
Replies
18
Views
4K
Hi there, I'm needing some guidance in how to interpret this reference method. How could one be sure that the installed cable behind the...
Replies
3
Views
2K
Evening all Just wondering what would be the reference method given for a twin and earth cable in a cavity wall without insulation....I...
Replies
3
Views
2K
evening all I am wondering what the installation methods should be for cables run under floor boards and then into stud walls but without thermal...
Replies
3
Views
7K
I wonder if anyone could assist with this query please ? I am a newbie, so any guidance or alternatives would be greatly appreciated. I need to...
Replies
6
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock