I have a very strange repeated RCD tripping scenario, which appears to suggest that two unrelated circuits are connected. Any problem solving thoughts would be appreciated.

I have an electrician who has done several jobs for us (new lighting circuits, appliance installation, outside lights, changing sockets etc). I am very pleased with him, and he has visited around 5-10 times over the last year to try and fix this - but admits he doesnt understand it. He is going to bring in colleagues who specialise in troubleshooting. So we both just thought it might help to put the problem out there for any ideas. I do not touch anything electrical myself.

New build detached house, finished 2012. Dual split load consumer unit with RCD on both (picture). Everything worked fine until last summer when Air COnditioning installed by very experienced professional firm. They installed 5 split units in 5 rooms, and put two outside Mitsubishi units each with new dedicated supply with MCB in CU in two spare slots.

Ever since then we have had intermittent RCD tripping, which my electrician has investigated extensively. Coincidentally we have also replaced all appliances since then with new Miele ones and new Liebherr high end fridge, so unlikely they would be involved.

More recently the RCD repeatedly trips unless the MCB for one of the air con circuits is switched off . Both the electrician and air con company have investigated this - but cannot find a fault with the air con circuit. However my electrician when checking all the possibilities discovered a very strange anomaly. First there is a 6 gang double pole grid switch in the kitchen for isolating various appliances (picture). He found that one of them (for plate warmer) had incorrectly had a simple (light) switch installed - so live and neutral were connected when on. He replaced that and checked all the others.

He then made a discovery which is hard to understand. The RCD immediately and repeatedly trips when the air con MCB is switched on. However it does not trip when air con MCB is on but dishwasher grid switch is off. Turning the dishwasher grid switch on immediately trips the RCD. The air con works fine and no RCD trip when dishwasher isolated, but dishwasher works fine and no RCD trip when air con isolated! We have repeatedly tested and found the same results.

My electrician is seeking advice but does not understand how a new air con supply can somehow be linked to the dishwasher which comes off the ground floor ring mains which has no connection to the air con circuits. Not only has he inspected and tested the CU several times but so have two very senior technicians from the air con company.

This all happens consistently including when all other appliances switched off, so I do not believe the supply is insufficient.

Hope this makes sense. I am not sure if posting pictures is allowed from new members, so I will try to do so in the next post.
 
my thoughts would be that both the dishwasher and the air con have appreciable earth leakage, each on it's own insufficient to trip the RCD, but together take it over the threshold. a ramp test of the RCD to see what it trips at, and an earth leakage clamp meter will help to resolve the problem.
 
Thanks both.

Puzzled that professionals havent excluded that.

The dishwasher was replaced during this period. So unlikely both old and new would be faulty in same way? I assume therefore the earth leakage is somewhere in the supply to the socket for the dishwasher?
 
I have Miele appliances and they have never caused problems. Disconnect the air con and see if it persists.
 
pleased with him, and he has visited around 5-10 times over the last year to try and fix this - but admits he doesnt understand it. He is going to bring in colleagues who specialise in troubleshooting.
may be the spark should have found the fault 2 time in ,do you not think so ,
by calling in colleague to trouble shoot for him ,if it was me, I would not have confidence with him with the spark you have now !
 
As the air con circuits are more recent I doubt they are interconnected with any existing circuit. I agree with Tel in #2 that the combined earth leakage of the equipment is tipping the rcd over the edge and this should be investigated as stated in #2.
 
Buzz - I agree. We will be bringing in someone new as well.

Also the air con company who I believe have good reputation, sent their 'most experienced' technician and they denied any problem with air con circuit, which doesnt appear to be consensus above. So that's two independent people who couldnt identify problem.

I am a doctor and we dont have a problem with getting second opinions for difficult cases - but I wont draw parallels between electrical circuits and the human body...
 
I am a doctor and we dont have a problem with getting second opinions for difficult cases - but I wont draw parallels between electrical circuits and the human body...[/QUOTE]

...and like doctors you can get good, bad and inexperienced electricians - you just haven't found a good one yet.

...and the human body is an electrical circuit.
 
He then made a discovery which is hard to understand. The RCD immediately and repeatedly trips when the air con MCB is switched on. However it does not trip when air con MCB is on but dishwasher grid switch is off.

You wrote the above. Is the RCD tripping when:

a. the (offending) a/c MCB is switched on - the other being off?

b. the(offending) a/c MCB is switched on - the other being already on?
 
Borrowed Neutral maybe??? did the A/C guys leave you any testing results or did they just install switch on an then leave.?
if it was that, maybe both RCDs would trip.just thinking aloud. but onlyif the N was fed from the wrong N bar perhaps.
 

Reply to Strange RCD tripping problem in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
553
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
735
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock