elsparko
doing an EICR today i could not take Zs readings at any sockets on various circuits protected by a RCD
tester set to low , no trip test and trips instantly on all 3 ciruits regardless of which socket i try result is always trip instantly
thought it could be the leads, wrong ports etc but everything is as it should be
auto test the RCD, all good 25.6ms @ x1 and 25.2ms @ x5
anyone had this happen before? logic tells me it is my tester at fault, kewtech
polarity is all good throughout the house so scratching my noggin a bit over this one