Discuss Strange voltages in the UK Electrical Forum area at ElectriciansForums.net

D

Davidobaynes

Evening all,
At work today we energised the newley rewired lighting circuit, only to find that from 3 lighting points onwards, the lights didnt work. Thought maybe disconnected neutral or line conductor. This was not the case, all connections sound.
Disconnected the neutrals at the 4th light and found 60v on one neutral and 230v on another. Replaced the cable between the 3rd and 4th light, so at the 4th light there should just be the line and neutral from the working 3rd light and the line and switch line down to switch. But the 4th light still did not work.
Any ideas ????
 
found 60v on one neutral and 230v on another.
60
Volts is an unlikely result. Try measuring it again with an analogue tester (assuming you were using a digital one).
230 V on the neutral suggests a bad neutral connection somewhere in the circuit.
 
Was it 230v on the "Neutral" going to/coming from light no.5?

If so, think about it.

Run a temp neutral cable from light no2 to light no 4
 
I reconnected the line and neutral to the 5th (so the rest of the lights on the circuit were reinstated) and none of them still worked but still had these voltages, this is the 1st fault to beat, not happy haha
 
My apprentice did some more fault finding on the circuit and he said he found, he had the neutrals disconnected at the 3rd light but he was still getting voltages at the 5th light neutrals, im not sure if this was correct but will check tomo
 
Its 3 plated, think ive just gotta work through the circuit light by light, annoying though because all the fittings look to have gd connections and look sound, will be sumthing simple though i bet
 
Sounds to me like you have the feed t+e cable out crossed with the switch t+e cable and the strange voltage is coming through the lamp. Does the strange voltage disappear if the lamp is emoved from the fitting?
 
May be they don't have a wander lead or don't realise what a time saver it can be in such situations.
well then they get a bit of 1.0 flat twin....do an end to end on it...null it out...and use that....1 end grabbed in the croc...the other end they terminate....a more time consumin way of doin it i know....
but why can`t some folk think on their feet...
 

Reply to Strange voltages in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, have an old bathroom fan. Which has two wires the black and red (line and neutral). The fan has no isolator switch and was powered when the...
Replies
3
Views
638
Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
575
Evening all, I had a quick Friday afternoon domestic job that has turned into a PITA and I'd appreciate your help. While adding some new lights...
Replies
10
Views
827
Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Replies
2
Views
537
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
575

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock