Hi all,

Just running through the "Photovoltaics in buildings guide - 2nd edition", as you do, and can't get my head around the string cable requirements.

p 16, 2.1.5 says:

"For a system of N parallel connected strings, with each formed of M series of connected modules, string cables are to be rated as follows

a. Array with no string fuses (of three or fewer strings only)
Voltage: Voc(stc) * M * 1.15
Current: Isc(stc) * (N-1) * 1.25
b. Array with string fuses
Voltage: Voc(stc) * M * 1.15
Current: Isc(stc) * 1.25"
Are the Current ratings there not the wrong way round? - if I have 1 string then I use the calc's in 'a.' so the rated current would be zero (i.e. Isc(stc) * (1-1) * 1.25).

Cheers
 
No, they're correct but only applicable to parallel connected strings (ie. more than 1)

a. basically says that each string cable has to handle the maximum Isc from all the other strings it's paralleled with being dumped down it in the event of a short on that string.

b. says that a string cable only has to cope with the max Isc of it's own string 'cos the fuses should protect it from fault currents from those around it.

On a domestic system string fusing is unlikely to be an issue as I don't think you'd ever go over 2 strings. On much bigger systems, with judicial choice of inverter and module, it's possible to avoid the need for them quite often.
 
Thanks there.

I figured a. was saying if you have "3 or fewer strings" in an array you don't need to install fuses. And to work out the Current Rating in that situation you use the formula given there "Isc(stc) * (N-1) * 1.25", where N is the number of strings. But with just one string then N=1 so that formula zeros out!

The formula in b. does work where N=1 tho, and the formula in a. does work for any number of strings greater than 1 - hence my thinking they got the formula's the wrong way round!? i.e. formula b. should be for 3 or fewer strings and formula a. is for 4 or more..

I'm missing a point here somewhere eh?lol
 

Reply to String fuses in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

A question/advice requested re: solar panels (the context is a van/motorhome conversion)... I've got a question re: fusing/breaker for a solar...
Replies
1
Views
2K
L
4kwp array. 20 degree pitch. Two Strings. Data below taken on a clear sunny day, the system is under load/generating. My problem is I can't work...
Replies
3
Views
1K
langstroth2
L
Another long one from me ... I hope that it covers all the bases and is a more thorough approach to the subject. It is my first design work so...
Replies
44
Views
6K
N
Have inspection soon and have done my install on my own house.Can someone please help with array test sheet. module is upsolar 240x7 one string...
Replies
9
Views
6K
jord35davies
J
My brain is overheating trying to make sense of PV panel parameters and calculate the CSA of a DC feed cable to the inverter. For my 16 HL Solar...
Replies
29
Views
12K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock