Hi all I have just had a 3920KW Sharp 16 X 245W panels fitted with a Solar River SR4K4TLA1 inverter.
There are 2 strings. One is currently reading around 330V and the other is just below 200V.
6 of the panels are landscape and 10 are portrait. I have since found out that 6 are on one string and 10 on the other.
Will that effect anything do you think or should the strings be matched in terms of input Volts.
The SolarRiver Product manual suggests that MPPT voltage range is between 200-500 V. The maximum DC Voltage is 550V. So therefore one of the strings falls below this minimum of 200V
Can anyone shed any light??