Posting a message to the forum will remove the above advertisement
  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.

Discuss Sub-mains earthing question in the Electrical Forum area at ElectrciansForums.co.uk.

Thread Status:
Not open for further replies.
Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. Lionscourt
    Offline

    Lionscourt EF Member

    I’ve recently run a supply to a garage and I had a question concerning the earthing. Here is the situation:

    TT supply to house.
    Supply goes into a time-delay 100mA RCD before it splits.
    This then goes through a sub-mains isolator at the house.
    3-core SWA runs about 60 metres to garage.
    17[SUP]th[/SUP] edition consumer unit in the garage.
    New earth spike installed for supply at the garage.

    So, my question: Should the SWA section be connected to earth at both ends, or only at one? Is there a reason I would NOT want to connect the earth at both ends?
     
  2. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    i would connect at both ends. that way the connection between the 2 rods should bring the Ze of both down.
     
    • Like Like x 2
  3. Amp David
    Offline

    Amp David Forum Mentor

    Location:
    Glossop
    Is there not any overcurrent protection for the sub main then?
     
  4. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    didn't spot that. isolator need to be fused to protect the SWA.
     
  5. Lionscourt
    Offline

    Lionscourt EF Member

    The sub-mains isolation is currently a BS 60947-3 along with a BS 60898 MCB. Are you saying that it must be something like a BS 88 then?
     
  6. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    no, the 60898is fine. it's just in your post 1 you didn't mention overcurrent protection for the SWA.
     
  7. clive dobbs
    Offline

    clive dobbs Guest

    Hi
    As it's a TT system at origin no problem connecting SWA earth at both ends, as mentioned before would help your earthing value. But if your origin earth was PME for example, then the SWA wire from origin should be earthed but not be connected to the consumer unit in the Garage, that should be earth free of PME, then the earthing arrangment for the Garage would become TT from the earth electrode allready installed.
     
  8. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    why??? what's wrong with the PME in the garage?
     
    • Like Like x 1
  9. clive dobbs
    Offline

    clive dobbs Guest

    Nothing in princible, but the example above, running 60 meters and a new consumer unit to a garage could require a bond to a water supply or any other extraneous conductive parts therfore that could introduce a potential back into the PME zone. If the cable was 3 core 10mm then bonding requirments for 100amp PME supply would be ok
     
  10. Lionscourt
    Offline

    Lionscourt EF Member

    Thanks for the comments everyone, they're appreciated.
     
Loading...
Similar Threads - mains earthing question Forum Date
Problem with mains outside light, any help please? Electrical Forum Sunday at 5:28 PM
Converting Tube Heater Socket into Mains Socket Electrical Forum Mar 5, 2019
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job