colin_scuba

6 apartments on 3 floors being fed from switch room in cellar, maximum rating 80amp.
Can I use 16mm twin and earth as oppossed to armoured to save on costs?
 
You need to assess the cable install methods and whether you require mechanical protection to void a 30mA front end rcd been a discrimination issue to the rcd's in the sub DB.. not fitting rcd coverage in the sub DB will be poor design as any earth fault would render the whole flat without power and resetting would be remote to the flat.

SWA with HRC fuse to 17th consumer unit is the best way and better for future proofing with less issues all round regardless if T&E is all surface and RCD not required.
 
sub mains
will be run up a riser then into the ceiling to the consumer unit

This still dosn't answer what i asked 'Does it require mechanical protection' be it in the short run from the ceiling to the DB or from the source to the riser.

Also regarding the ceiling run i hope you have factored insulation into the equation if it will ever be fitted even at a future date (ignore if not a factor). If it is a thought then the cable size seems a little on the small side although info is limited.

Lastly what about your earth conductor CSA ensure you comply to BS7671 additional earth conductor may be required with the T&E option.
 
If we are going to use T+E then we are going to run a 10mm supplimentary
but I thinking of going for the option of armoured for the reasons you stated.
 
If we are going to use T+E then we are going to run a 10mm supplimentary
but I thinking of going for the option of armoured for the reasons you stated.
and i doubt 80A will cut it either for 6 apartments.

i mean are there going to be any electric showers in these apartments?

- - - Updated - - -

what have you got coming in at the switchroom?
 
Sorry may have have been discussed but need to verify earth will be big enough if using T&E as I have encountered issues with this method where earth cable was to small
 
There is no electric showers there will be run off the boiler and now they are using gas for the cookers.
There will be 2 lighting, 2 ring mains and 2 16amp radial circuits max run is 45m . sub mains that is
 
There is no electric showers there will be run off the boiler and now they are using gas for the cookers.
There will be 2 lighting, 2 ring mains and 2 16amp radial circuits max run is 45m . sub mains that is
well..
going by the finals in each apartment...comes out at 108A..
lets apply some diversity:
this number X.2 given that there wont be much usage of anything heavy in here by what you have said regards spec=21.6A...
so can you see that even with a very harsh diversity applied of .2 you will still be struggling at 80A..

you will need more juice than you are allowing for i`m afraid...
 
Is this all foor renting out or is there any possibility, however remote, that they will be sold?
If so you should be looking at wiring in a way that could be adopted at a later date by the leccy board.
IE 16split on tray for example.

Boydy
 

Reply to Sub mains in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
Hi, I have been tasked with a kitchen rewire. The current DB is fed by a 16mm armoured. There is a split load old contactum DB which I don’t...
Replies
4
Views
1K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
Good morning all, long time reader first time post so looking for some help I’m qualified as an electrician but haven’t worked as a sparky for...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock