Posting a message to the forum will remove the above advertisement
  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.
  2. angel While you're here, would you mind checking out our Electrician's Insurance section to see if we could save you a few quid? - Specifically our Van Insurance Deals and Public Liability Insurance Deals. Thanks for supporting the forum! angel

    5% Discount from Electrical2Go.co.uk for ALL members! - Click Here

Discuss Submain Supply 100a 100mA in the Electrical Forum area at ElectrciansForums.co.uk.

Tags:
Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. Tom Christopher
    Offline

    Tom Christopher EF Member

    Location:
    Dorset
    Business Name:
    DC Electrical
    Installing a 25mm 3core swa to feed an exisitng consumer unit due to the SEB moving the supply.

    Planning to use a 100A 100mA time delayed rcd to feed the split load rcd board.

    Sound ok?
     
  2. Ian1981
    Online

    Ian1981 Electrician's Arms

    Location:
    North east
    Why a 100mA S type rcd upfront?
    Is it a TT system?
    Will the dual rcd board accommodate a 25mm into the earth bar?
    Will there be a switch fuse isolator fitted If the supply is over 3 meters from the cut out?
     
    • Like Like x 2
  3. Dillb
    Online

    Dillb Electrician's Arms

    Location:
    Nottingham
    Why would it need that? Nothing in BS7671 about it, and the DNO may not specify it.
     
    • Optimistic Optimistic x 2
  4. Ian1981
    Online

    Ian1981 Electrician's Arms

    Location:
    North east
    433.3.1 item (iii)
    A device for Overload protection need not be provided at the origin of an installation where the distributor provided an overload device and agrees it affords overload protection to the part of the installation between the origin and main distribution point where further overload protection is provided.
    The general consensus is that the DNO will allow 3 meters and no more for their cut out fuse to protect the tails.
    Also 434.3
     
    • Like Like x 1
  5. Dillb
    Online

    Dillb Electrician's Arms

    Location:
    Nottingham
    So as I say its speculation if its needed, nothing to say in this instance that the DNO require it fitting.
     
  6. spinlondon
    Offline

    spinlondon Trusted Advisor

    Location:
    Harlow Essex
    My understanding is that the DNO will not generally allow their fuse to be used to protect any part of a consumer’s installation.
    The 3m stipulation relates to the BS7671 requirement that overload protection must be provided within 3m of a reduction in the CCC of a conductor.
     
  7. Ian1981
    Online

    Ian1981 Electrician's Arms

    Location:
    North east
    This is northern powers requirements anyway 1388B8A2-0046-4E6C-88C4-944582FF8636.png
     
    • Like Like x 1
  8. Tom Christopher
    Offline

    Tom Christopher EF Member

    Location:
    Dorset
    Business Name:
    DC Electrical
    PME

    Yes dual board will take a 25mm

    SWA will be made off into a metal enclosure with the 100a 100ma time delayed rcd. This will be mounted next to the main supply, so tails less than 3m

    SWA will be above the plaster board so wont it need rcd protection?

    I thought time delay to save both RCD trippings if there is a fault?
     
  9. Ian1981
    Online

    Ian1981 Electrician's Arms

    Location:
    North east
    Tho that is a regulation in the context you describe that has Nothing to do with the DNO tails
    Read 433.3.1 and 434.3 or not
     
    • Agree Agree x 1
  10. spinlondon
    Offline

    spinlondon Trusted Advisor

    Location:
    Harlow Essex
    RCD protection for cables concealed above ceilings and below floors is not an acceptable method for providing extra protection.
    SWA however is.
     
    • Agree Agree x 1
  11. spinlondon
    Offline

    spinlondon Trusted Advisor

    Location:
    Harlow Essex
    Not aware we were discussing DNO tails?
    BS7671 does not apply to DNO equipment.
     
  12. Murdoch
    Offline

    Murdoch Electrician's Arms

    Location:
    Woking
    ^^ swa doesn’t need rcd ...
     
    • Agree Agree x 1
  13. Andy78
    Offline

    Andy78 Trusted Advisor

    Location:
    Kingston upon Hull
    There is no need for RCD protection for those reasons if using earthed SWA. If it did, then you RCD you selected would not have been suitable anyway.
     
    • Agree Agree x 2
  14. buzzlightyear
    Online

    buzzlightyear still kicking sand, before pushing up daisies . Electrician's Arms

    Location:
    star command
    new sub mains from tncs to tt then .
     
  15. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    We can only confirm if this is okay if you let loose what the earthing system is.
     
    Last edited: Jun 25, 2018
Loading...
Similar Threads - Submain Supply 100a Forum Date
Cu change with swa submains...20 characters! Electrical Forum Jul 9, 2018
10mm t&e submain cpc Electrical Wiring, Theories and Regulations Jun 13, 2018

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job