    Evening, may I pick you brain guys?
    I have wired a summer house about 30m away from the main board. I have used 32A at DB1 (not RCD protect) and 6mm² 3core SWA, where I have connected both black and sheath (sleeved) at both end as CPC. In the Summer house I have used shed consumer unit 1xRCD and 2 useable mcbs.
    I test Ze and PFC at DB1. I then move to test the shed DB2 RCD, Ring final and light circuit.
    I am wondering
    1. if I use Zs at the DB2 as Ze while filling the cert or do I use Ze and PFC from DB1?
    2. I have added a 32A mcb at DB1, do I test the whole DB1 or Ze and PFC from there are enough?
    What are your thought guys?
    Regards
     
  2. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Staff Member Moderator

    Location:
    Northamptonshire
    Ze and PFC are done at source, Ze only occurs at source assuming you have not TT'd DB2. There is no need to test all circuits from DB1, just your new circuit.
     
    • Like Like x 1
  3. ferg
    Offline

    ferg Electrician's Arms

    Location:
    N.W.Scotland
    One section of the EIC is for supply characteristics and the SOTR is ZS and IPF at DB
     
  4. Gakure
    Offline

    Gakure Regular EF Member

    Location:
    kent
    Thanks ferg
     
  5. Gakure
    Offline

    Gakure Regular EF Member

    Location:
    kent
    Thanks Westward
     
    • Like Like x 2
  6. Welchyboy1
    Offline

    Welchyboy1 Electrician's Arms

    Location:
    Essex
    Usually on the top of the test results section page of the cert there is a box for zs and ipf reading at origin of your remote 2way cu, but this is only on the last test results page, its always worth measuring these values as part of your testing imo
     
  7. Gakure
    Offline

    Gakure Regular EF Member

    Location:
    kent
    Thanks guys, just to clarify, am looking at the test sheet part 10, I can see PFC bit and a column of Zs measure near the end of RHS.
    I am wondering am missing the Zs box
     
  8. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    What/whose forms or software are you using?
     
  9. Gakure
    Offline

    Gakure Regular EF Member

    Location:
    kent
    Niceic 18th edition
     
  10. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    Is it the online software?
     