Discuss Sunny Boy 4000TL Multi Function Relay in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

O

Orty

View attachment img116.pdf
I am about to replace my 3Kw Immersion Heater with a 1.5Kw. Please see the attached PDF
I intend to control it with the multi function relay in the Sunny Boy turning on at 1800w. The default setting for self consumption is 1500w
The other settings I am considering altering are the default 30mins for start up power to 15mins.
The original IH timeswitch will be left in circuit for manual/timed operation and the Sunny Boy will overide this.
Has anybody any comments to make on my proposed system please.

Thanks

Orty
 
Last edited by a moderator:
I spy a contactor in his diagram.

The circuit is fine in principle, in that it would work. What you could do is think through where you have isolation/fusing/mcb. It is always tricky when you have something that can be powered from x2 routes, but you do not want the second route energising unexpectedly whilst someone is working on it.

Personally I would keep the 'control' aspects and 'power' aspects separate. So:
- single mcb runs the whole lot
- fused spur for the control elements of sunny boy and timer
- timer powers the contactor coil rather than the immersion direct
- if the connection to the sunny boy cannot be safely unplugged at the sunny boy to isolate, then put in an isolator.

Regards
Bruce
 

Reply to Sunny Boy 4000TL Multi Function Relay in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

O
I know this subject has been covered many times but my simple question is: We use an oil fed boiler for central heating to our home and for hot...
Replies
27
Views
26K
Hi Folks – there has been a lot of info re Immersion Heater Controllers on this forum and as I was updating and drawing up the circuit etc I used...
Replies
0
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock