What code would you give when doing EICR for a property that has no supplementary bonding in a bathroom, there is no RCD on any circuit but zs and insulation tests are good,

Is it acceptable to measure the resistance between the shower and pipework, if it's under 0.05 ohm's take it as bonded, incase the bonding had been done but covered up?
 
I Would and have C2 'd a room containing a bath or shower that has no suplimentary bonding and does not have rcd protection if there is an electric shower.

However I do like essex's take and would consider If it has no electric shower and no class 1 electrical fittings I think I would C3 it in future.
 
Bathroom has an electric shower, so hoping I can bond from CPC to pipe inside the shower, and that the shower pipe is accessible under bath and use that to bond hot and cold bath taps then take across to sink, also bond from shower isolator pull cord to light pull cord which will intern bond light fitting,

maybe easier to install an RCD
 
Bathroom has an electric shower, so hoping I can bond from CPC to pipe inside the shower, and that the shower pipe is accessible under bath and use that to bond hot and cold bath taps then take across to sink, also bond from shower isolator pull cord to light pull cord which will intern bond light fitting,

maybe easier to install an RCD

You may want to think again. If the shower is plastic then what are you hoping to gain from cross-bonding the CPC to the pipe work?

Are the lights, pull cords, isolator also metallic? If not again, what do you hope to gain from cross-bonding to these?
 
I see what you mean as no exposed conductive parts on shower or pull cords

my idea was to avoid running a cable from the floor to ceiling and that cross bonding the CPC's in pull cords would help lower the resistance between them, now thinking code 3 would be adiquet
 
Last edited:
You may want to think again. If the shower is plastic then what are you hoping to gain from cross-bonding the CPC to the pipe work?

Are the lights, pull cords, isolator also metallic? If not again, what do you hope to gain from cross-bonding to these?
Oh yes! let's all go back to the good old 15th Edition.:eek:
If he wants to bond the rads, I'm sure I still have the odd one of those special earth bond clips for 'em.:cool:
 
What code would you give when doing EICR for a property that has no supplementary bonding in a bathroom, there is no RCD on any circuit but zs and insulation tests are good,

Is it acceptable to measure the resistance between the shower and pipework, if it's under 0.05 ohm's take it as bonded, incase the bonding had been done but covered up?
 
Even if the pipework is all plastic, all circuits serving the location are required to have supplementary bonding between them , whether of class 1 or class 11 construction if no rcd is present to the circuits serving the location.
See gn7 and gn8 for examples of such a set up
 
Even if the pipework is all plastic, all circuits serving the location are required to have supplementary bonding between them , whether of class 1 or class 11 construction if no rcd is present to the circuits serving the location.
See gn7 and gn8 for examples of such a set up

701.415.2 clearly states only ‘extreneous-conductive parts’ and ‘metallic pipes’ are to be supplymentary bonded.
 
Even if the pipework is all plastic, all circuits serving the location are required to have supplementary bonding between them , whether of class 1 or class 11 construction if no rcd is present to the circuits serving the location.
See gn7 and gn8 for examples of such a set up
From an interest point of view Ian do you have a Regulation number to clarify this statement? I don't have any GNs.
 
If rcd protection is not present then you still need to ensure that any touch voltages between circuits is at a minimum under fault conditions by supplementary bonding the circuits in the location
 
If rcd protection is not present then you still need to ensure that any touch voltages between circuits is at a minimum under fault conditions by supplementary bonding the circuits in the location

What touch voltages would you expect between a metallic light and a plastic pipe?
 
What touch voltages would you expect between a metallic light and a plastic pipe?
Why do you think we need to ensure that everything is at the same potential in the location regardless of metallic pipes or class 1 or 11 equipment installed without an rcd?
Shouldn’t need spelling out
 

Reply to Sup bonding code for property with no rcd in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello. Non-electrician here. Failed an EICR yesterday as the electrician graded my consumer unit C2. Why C2 and not C3? He didn't say (and still...
Replies
22
Views
3K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
778
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Replies
4
Views
2K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
I am reviewing a EICR for a property I am buying. The vendor has had the EICR done, but both the Cooker and Shower are on 40A 60898 B curve mcbs...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock