Hello all,
Perhaps a few of you could help my understanding of the following query.
The situation I am about to describe is purely hypothetical to help my understanding of the issue.

Let's assume within a domestic bathroom, I have a combination of exposed conductive parts and suspect extraneous conductive parts which can be accessible simultaneously, lets also assume the circuits within the bathroom achieve ADS, and are covered by a 30mA RCD, and that main bonding to incoming services has been carried out. I want to check to see if supplementary bonding is required to the suspect extraneous metal pipe.
Am i correct with the following assumptions:

>25000 ohms: is the resistance of the metal pipe to the exposed metal and of that to the MET. conclusion ; the pipe is deemed NOT extraneous and therefore no bonding required.

<1666 ohms: is the resistance of the metal pipe to the exposed metal and of that to the MET. Conclusion ; the pipe IS deemed extranoues, but the resistance is low enough to achieve a speedy disconnection time, so no bonding is required.

>1666<25000 ohms : is the resistance of the metal pipe to exposed metal and if that to the MET. Conclusion ; the pipe IS deemed extraneous and bonding required.

I have also seen the figure 0.05 ohms when referring to supplementary bonding, I'm not quite sure what this refers to. The minimum resistance required once the bonding is in place?

Thanks in advance.
 
Think the figure of 0.05 is used so that continuity can be reasonably assumed between any two points of metallic pipes
That figure is used in guidance note 3 but not in bs 7671 that I can recall anyway.

Maximum resistance between bonded pipework and all bathroom circuits 30mA rcd protected would be 1667ohms so the touch voltage doesn't rise above 50v.
50/0.03=1667 ohms
 
One of the problems I have with the table from the OSG, is with the column for bonding two circuits together.
My understanding, is that where two circuits have CPCs of different CSAs, then the bonding conductor should be the same CSA as the smaller CPC with a minimum CSA of 4mm2 if not mechanically protected.
i.e. where the CSA of the lighting circuit is 1mm2 and the CSA of the shower circuit is 6mm2, the CSA of the bonding conductor only needs to be 1mm2 or 4mm2 if not mechanically protected.
 
One of the problems I have with the table from the OSG, is with the column for bonding two circuits together.
My understanding, is that where two circuits have CPCs of different CSAs, then the bonding conductor should be the same CSA as the smaller CPC with a minimum CSA of 4mm2 if not mechanically protected.
i.e. where the CSA of the lighting circuit is 1mm2 and the CSA of the shower circuit is 6mm2, the CSA of the bonding conductor only needs to be 1mm2 or 4mm2 if not mechanically protected.
The minimum size supplementary bonding conductor size allowed is 2.5mm with mechanical protection with a circuit cpc size of upto 4mm2
 
Yes, if it's two extraneous parts, then 2.5mm2, but it would be very rare that there would be mechanical protection.
Some boxed in pipes in a bathroom perhaps?
If there's a CPC involved then it's the CSA of the CPC, but I can't see why it should have to be the larger CPC that determines the CSA.
 
Thanks for those videos Midwest, especially the first one, also John ward has some useful videos, and thanks Ian for clarifying 0.05.
Although comments on CSA of conductors wasn't really what I was after.
 

Reply to Supplementary bonding in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Just had my design project handed back to me from my last block and I got everything right apart from one question Q9 I would take a photo but...
Replies
3
Views
1K
A technical question: Regulations require us to bond extraneous parts back to the MET with an appropriately sized bonding conductor. I don't...
Replies
10
Views
2K
A 'Sunday challenge' for the qualified electricians.... Can anyone explain why a built-in gas meter housing box that is located 600mm above a...
Replies
8
Views
6K
Yes, still doubting my own judgement when it comes to supp bonding and EICRs, so would welcome any thoughts on the latest one. Newish flat...
Replies
6
Views
1K
Yes, it's another EICR coding question - hurrah! :blush: Inspecting a small 1 bed 70s ex-council flat that was going well. Main Bonding had...
Replies
12
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock