Guys did a consumer unit change over the weekend and hit 2 snags
1. The suppliers cut out fuse has no markings on it ie no BS 88 60 amp instead the unit is black with no markings on it so how to I id it for the cert. The property is a 3 bedroom 1950s flat TNS supply.


2. Maximum demand I have 40A shower 32A cooker 32A ring 32A ring 6A lights 6A lights so what should my figure be ?

thanks in advance
 
It does sound like a BS88, so put that in the box.

To work out your maximum demand add the MCB ratings together and times it by 0.4, and put that figure in the box.

cheers....................Howard
 
Check for the info on the previous certs or inspection reports----:D...sorry oldtimer just being silly

do as SkB advises these details .although necessary,are not too crucial afterall
 
To work out your maximum demand add the MCB ratings together and times it by 0.4, and put that figure in the box.

cheers....................Howard

take the highest rated mcb add up the rest then times them by 0.40 and add the highest breaker to that.


32A cooker 32A ring 32A ring 6A lights 6A lights = 108x0,40 = 43.2

+ 40A shower =
83a
 
Last edited by a moderator:

Reply to suppliers cut out fuse in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K
  • Locked
So, a flat 6 floors and above needs an AFDD on each socket circuit. At up to £150 each it is going to be an expensive undertaking if there are...
Replies
21
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi all, I have a regular client who has asked for a battery back up system to be installed at their home. They live in a rural location on a...
Replies
2
Views
1K
I'm always in a dilemma with regards max demand. Often you work it out and it's higher than the the 80A or 60A cut out fuse. However, you know...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock